Morning all,

I have been to look at a job this morning to rewire a radial feed supplying two socket outlets off a 20 mcb. The cable from the board is a black pvc 2 core cable(does not look like copper) and has a separate earth run back to the met.
I am currently doing my 2392 and hope to start doing eicr when I have finished this course. I was wondering what code you would give for this? Assuming that r1/r2 , I/r were okay. Would it be c3 improvement recommended

thanks
 
Are you sure it's pvc.

Two core black was commonly trs, or latterly polythene, both using the old colour scheme, in imperial sizes and tinned copper.

No cpc would put it pre 70's
Polythene would be pre 70's
TRS would be pre 60's

If the outer is dull black likely to be TRS, if shiny/waxy - polythene.

There is no requirement that the cpc be integral to the cable, so no code, however given the age and potential condition of the cable itself this may be anything from C1 to C3 as TRS can flake off exposing the live conductors.

It would be the cable condition that would concern me.

(And potentially the age of the installation, - it needs a good coat of looking at)
 
Morning all,

I have been to look at a job this morning to rewire a radial feed supplying two socket outlets off a 20 mcb. The cable from the board is a black pvc 2 core cable(does not look like copper) and has a separate earth run back to the met.
I am currently doing my 2392 and hope to start doing eicr when I have finished this course. I was wondering what code you would give for this? Assuming that r1/r2 , I/r were okay. Would it be c3 improvement recommended

thanks
What size is the earth cable going back to the MET
 
I'm another one curious about the size of the earth cable.
 

Reply to Wife Code for black pvc with separate earth run to socket? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
655
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
918
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
921
Hi everyone Just looking for a little advise on if my plan to run this spur is okay I’ve drawn a diagram in hopes to make my expiation simpler...
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock