Well he ain't doing it proper like is he?Hi guys R1+R2 on a eicr mates tutor on the 2395 course said no need to carry out just zs is enough and on ring just end to end readings what's everyone's thoughts on this
You asked for opinions or thoughts file:///C:/Users/Pete/Downloads/Best-Practice-Guide-4-Issue-4-.pdfWhat you mean proper this is coming from teacher teaching the 2395 said it's a good thing but unnecessary just zs is enough
The Tutor said Zs and end to end tests NO R1+R2 required, or at least that's what I think the OP means. You have to ask yourself, why does the EICR form have slots for R1+R2 if it's not required, odd that Westy.What does he mean just Zs, no other tests on the ring final, not even an end to end check.
But in real life in the event of a fault parallel paths would be included no?On a ring final circuit, does this mean just measuring r1, rN, r2 - and nothing else? Or does he mean Zs (at every outlet) plus r1, rN, r2?
If you measure Zs rather than (R1+R2), then you are not going to know for sure (R1+R2), you can't just subtract Ze (at least if you want to do it properly, and be sure you aren't including any parallel paths due to bonding etc.).
r1 r2 rn and zs at every accessible pointOn a ring final circuit, does this mean just measuring r1, rN, r2 - and nothing else? Or does he mean Zs (at every outlet) plus r1, rN, r2?
Then again they should have didn't types for dThe Tutor said Zs and end to end tests NO R1+R2 required, or at least that's what I think the OP means. You have to ask yourself, why does the EICR form have slots for R1+R2 if it's not required, odd that Westy.
can you please clarify the reason of R1+R2? Think I'll give nic ring see what they have to sayWell I'm not sure the tutor would pass his 2395 doing it his way!
Just because an installation is energised doesn't mean it is installed to regulations.
I totaly agreeWell I'm not sure the tutor would pass his 2395 doing it his way!