Toneyz
It is as the name surgests a report on the condition fully or in part of the electrical installation at that time and can be used to see if the installation has deteriated since the last .
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss eicr in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Replies to date just go to show how this is interpreted. GN3 guide for me.
But I suspect that a considerable amount of testers don't do full dead tests as part of the eicr.
Just trying to show the OP the correct procedure for testing RFCThat is for testing a new install covered under 2394 not 2395 which is periodic there are diferent requierments, it is down to the tester what test needs to be carried out and agreed with the customer and clearly stated on the cert
You should at least do an end to end test and a figure of eight, this should give a rough indication of the Zs.
That fence they sit on must be well worn.Spoke to the nic he said no two places are the same it's about your feel on the installation if you find there as been alteration then do it if you feel it looks good readings good end to end then it's ok all bout your professional judgement I think I'll carry on doing it the way I have been all test that's involved just bit shocked what some colleges are teaching
Again I would point you to the guidance in Guidance Note 3 which suggests that a full continuity of ring final circuit conductors test may not be warranted or necessary where records exist for existing ring final circuits and where no alterations to that circuit have been made. Again, like I said, end-to-end tests on the circuit conductors would seem to be reasonable in these circumstances. Obviously the Zs of all socket outlets should also be verified.However, it doesn't prove any of the above. Only the 3-stage RFC testing procedure can, hence why we do it in the first place.
Carry out an eicr with minimal disruption and dismantling whilst verifying the safety of the installation
( Guidance Note 3 which suggests that a full continuity of ring final circuit conductors test may not be warranted or necessary where records exist for existing ring final circuits and where no alterations to that circuit have been made)
How many domestic eicrs have you done where this paperwork was available AND no alterations were made. Fair enough, I'm new to the game, but I reckon it's not all that often anyway