16mm tails with 100A fuse ???
W
Wilko
Job today to change out old fusebox and I'd noted the 16mm tails but on pulling the fuse this morning it was 100A which I wasn't expecting. Fairly recent new smart meter installed by XYZ who are also the DNO ... Shouldn't the fuse be limited to 60A in this case? Thoughts and advice appreciated :)
Between meters and service terminal blocks they are, as soon as you contain them they are no longer clipped direct throughout and that rating will not apply.
Back on track - how difficult would it be to change the tails?
What do you estimate the maximum load to be for the property? If its well under 87 amps you could reasonably leave the 16mm in place ....
tin hat is on!
Its all about how the cable is installed and it's ability to dissipate heat.
Sorry but that's just another post meant quite frankly to annoy people
Quite the opposite it is a reasoned argument using as you say, how the cable is installed and it's ability to dissipate heat whereby this ability is lowered once contained.
If a cable passed directly through a insulation packed 4x2 stud partition so that those few inches were all that was not clipped direct,how many of you would de rate the cable?
Getting rid of that heat is what the ccc are all about as Ian mentioned previously
Well, I did try to move the tails but only got the 20cm I needed for the new CU and they won't budge any more, although there is slack at the meter. So changing the tails will be mission messy. Tails leave the external chest high meterbox in a cavity brick wall, go up and over the front door and drop down from the ceiling. CU mounted high up next to ceiling behind front door. New CU is in the location of the original fuse unit, at Customer's request. But somewhere in that lot the tails go through a beam I reckon and are jamming up. Nothing I can't sort if I rip into the plaster ceiling she's just had done :( .
In terms of load, I am sure a 60A fuse would be fine. 2BR mid terrace, newish combi for CH and HW. Biggest drain will be an induction hob she's got on order.
There's no insulation anywhere near the tails that I can see looking from both ends. The tails will be less than 3m long.
Wilko,
Pete999,