I have a three phase switch fuse supplying a 16A socket. In the specification provided it states the following:

Design Current - 16A
Main Protective Device 20A

The circuit is fed from a C20 MCCB at the distribution board.

What size of fuses should I be putting in the switch fuse?

16A or 20A?

Thank you.
 
Hi,

I have a three phase switch fuse supplying a 16A socket. In the specification provided it states the following:

Design Current - 16A
Main Protective Device 20A

The circuit is fed from a C20 MCCB at the distribution board.

What size of fuses should I be putting in the switch fuse?

16A or 20A?

Thank you.
Don't mean to be funny, are you an Electrician? do you have any electrical experience? sorry for the questioning but your profile reveals nothing.
 
Don't mean to be funny, are you an Electrician? do you have any electrical experience? sorry for the questioning but your profile reveals nothing.

I am a trainee electrician and it is a question asked today at college to which the discussion never revealed a correct answer, we thought that it would be 16A fuses due to it being a 16A socket.
 
I can't answer your question but I believe there is a trainee section that will be able to help with these types of question and many more that you may have without the snide comments ;o))))))

Good luck in your training, I'd just use Wriggleys chewing gum wrapping to be honest but then you won't pass any exams ;o))))))
 
Last edited by a moderator:
I can't answer your question but I believe there is a trainee section that will be able to help with these types of question and many more that you may have without the snide comments ;o))))))

Good luck in your training, I'd just use Wriggleys chewing gum wrapping to be honest but then you won't pass any exams ;o))))))
and of course, you leave the partly chewed gum in there as a flash guard, even though it's more hazardous than asbestos. i can honestly say, i've never got my shoe stuck in discarded asbestos.
 
I am a trainee electrician and it is a question asked today at college to which the discussion never revealed a correct answer, we thought that it would be 16A fuses due to it being a 16A socket.
Thanks Gavin, it makes it easier to answer that's the reason for asking
 
Yeah we are getting a fair few reports about the constant questioning of quals and empty profiles, maybe we could just start answering the questions with a relevant answer.
Cheers
GMES
Perhaps some discussions among staff members would be a good idea, all on the same page so to speak.
 
To the OP I believe if you look in GN1 it gives a suggested maximum overcurrent protective device of 20A. I believe this is due to the fact a radial of more than one 16A socket can be employed, after this 32A, 63A etc... are suggested to be single point radials with a protective device used to match their rating. If however the circuit supplies one 16A socket I see no reason to use anything above a 16A protective device.
 
this question is problematic.one would assume that the 16A circuit would be protected with a OCPD suitable for the cable and load. so 16A or 20A would be appropriate.however,you'd not achieve discrimination with the 20A MCCB. catch 22 here.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
GB

Thread Information

Title
What size Fuses do I require?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
32
Unsolved
--

Advert

Thread statistics

Created
Gavin Millar,
Last reply from
Wilko,
Replies
32
Views
3,868

Advert

Back
Top