Hi,

I have a three phase switch fuse supplying a 16A socket. In the specification provided it states the following:

Design Current - 16A
Main Protective Device 20A

The circuit is fed from a C20 MCCB at the distribution board.

What size of fuses should I be putting in the switch fuse?

16A or 20A?

Thank you.
 
Hi,

I have a three phase switch fuse supplying a 16A socket. In the specification provided it states the following:

Design Current - 16A
Main Protective Device 20A

The circuit is fed from a C20 MCCB at the distribution board.

What size of fuses should I be putting in the switch fuse?

16A or 20A?

Thank you.
Op no mention of cable size, ccc is a main factor.
 
...20A is due to the fact a radial of more than one 16A socket can be employed ... however if the circuit supplies one 16A socket I see no reason to use anything above a 16A protective device.
Agree.
Apologies for my dumb question but why are there additional fuses being spec'd here? Local isolation yes, but it's already got a C20 at the board so shouldn't the question be "do I keep the C20 or go to C16?" :)
 

Reply to What size Fuses do I require? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
545
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
465
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
603

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top