Use of 20AX switches in spurs off ring main
I bought a number of 20AX grid switches with printed labels on them e.g. washing machine. These were to put an isolator above the work top for a 13A switched socket under the work top in the utility room. Electrician says no as the spur will be off a 32A ring the switch must be capable of the ring rating not the spur (single 2.5mm2 T+E). I can almost see his point but most suppliers have a range of printed 20AX but none for 32A so you end up with an unlabelled switch or a stuck on label which is not great. Any views on this? Thanks.
So what does your electrician want? 20AX gridswitch into a fused grid module to protect the spur?
What you have described is fitted in millions of homes across the uk.
Its just like having a spur off a ring, which is perfectly acceptable and within regs - (as long as its only to one point), but the spur has an isolation switch.
The only reason to have a fused spur is if theres more than one point served from the spur, ie a radial circuit off a ring
Why? There is no requirement for isolators above the worktop, and they look so ugly.
Also why 13a switched socket as well as an isolator, surely an unswitched socket is better if you have isolators?
The best isolation is pulling the plug. If there is a fault you will need to move the machines anyway so pulling the plug is easy.
If an appliance is difficult to get out or is part of an inbuilt system then there should be a local means of isolation, this is not just for the electrical trade but others who are not so aware of the risks, the extent to this is ambiguous but with built in cookers, fridges etc it is recommended so any fault or concern electrically mean it can be safely isolated locally before removal by other trades, as an example of those not in the know how like plumbers.
It is not a requirement or really necessary as isolation can and should be done at the CU. Local isolators are not fitted in other countries and they don't have any problems.
"Oh no! Theres a strong burning smell coming from my washing machine.... What do I do?!!?"
"Quick, turn off the power... theres a switch marked washing machine"
"OK, got it.... Wow, that was so easy"
OR
"Quick, turn off the power... Uhhhh…. no switch? … Wheres the consumer unit!"
"Um... Its under the stairs.... behind the bucket... its in a little cupboard... You have to wiggle the latch to get the door open.. Its not got little flicky switches... just pull the fuse"
"Yeh… I think I got it.. which fuse?! Nothings marked!"
"I dunno!.... Oh no... flames!.."
Isolation switches;- Not a requirement, but damn convenient in a crisis.
Re the argument about above worktop isolators; a lot of my customers didn't like them, so a socket in an adjoining cupboard is sufficient.
Re the OP's question; App 15 is the informative guide to spurs off RFC. Would a 20A DP switch, followed by a 13A socket could be construed as more than outlet? Done it loads myself, but perhaps thats his sparks thinking.
Sorry but that’s not correct. They are required by Scottish Building Standards, so the statement isn’t actually correct.
Mandatory Standard 4
4.8.5 Access to manual controls
...Where sockets are concealed, such as to the rear of white goods in a kitchen, separate switching should be provided in an accessible position to allow appliances to be isolated.
Fixtures (sockets/switches) etc should be acted at lease 150mm above he worktop. (I've paraphrased that whole paragraph).
I appreciate you don’t have to fit them in England and Wales as far as I know? Either way it’s good practice for emergencies. I think little sparks comments are very pertinent. Do you not fit shower isolator switches in bathrooms or oven isolators in kitchens then?
To the op - if your electrician has an issue with the switches and the supply cable to the load not being protected why no incorporate a FCU module into the grid switch?
redbarnman,
Phillip,
