Hi,
Just need to check something. Sparky installed two new plug sockets. To do this, cut into the main ring, put a junction box in, one cable out to socket. Then from there connected one more plug. I understand to spur off a spur you should use a fuse between them?
As @Strima says.
Help an Aussie understand.
The fuse connected to the spur, where is that physically situated in the installation? alongside the outlet, back in the switchboard, or somewhere else?
and do you guys still use fuses, or is that your name for a breaker?
A ring circuit has two actives in the bottom of the main breaker and two neutrals in the neutral link?
To spur off a RFC with multiple outlets, you must have a Fused spur as the first outlet then your socket outlets as described in the diagram posted earlier, the fuse in question will be a cartridge fuse housed in the fused spur unit max size 13 Amps, hence the max allowed in the socket outlets you feed from that Fused spur unit will be limited to 13 Amps, the RFC may still be protected via a MCB at the CU, does the existing RFC have RCD protection? Hope that makes sense.
It makes sense (not that I think it is a great way of wiring a circuit). I know the logistics of it, I was more wanting the know the physical location of the fuse. So it is embedded in the socket?
Why are you still using fuses?
No Mate not imbedded in the socket The switched fused spur unit is a separate unit, roughly the same size as a socket, used for fusing down when you are connecting lower load, difficult to explain to a non Brit, the fi/use is of the type used in 13Amp UK plug tops, google "switched fused unit" it may explain "a picture is worth a thousand words" as they say
We use both fuses and circuit breakers. Any new consumer unit will be populated with MCBs or RCBOs. Appliance plugs and fused connection units will have fuses.
Fuses are also useful when you need discrimination between upstream/downstream devices.
The fuse is not embedded in the socket, it is held in a faceplate accessory which has the same dimensions as a standard 13A socket outlet.
Hi,
Were the sockets singles or doubles? Whilst not technically correct it would be acceptable in practice if both sockets were singles, as this would be no different to a double socket on a spur.
No it isn't technically correct at all. I understand your theory but nevertheless it is incorrect advice.
I said it is not technically correct. But if I was doing an EICR two doubles on a spur would be a code 2, two singles would be a code 3. If two singles were butted together they would look like a double, a couple of meters of cable between and suddenly it's a different ball game. Not saying it's compliant but in practice there is no difference whatsoever, the regulations are not statutory and deviation can be justified where equivalent safety is achieved.
You said not technically correct but acceptable. A two gang socket is type tested with a load of 20A (14A and 6A) across the outlets and whilst in practice this may not be the case it is fact. Based on this a two gang socket will draw no more than 20A, argue this with British Standards. Two one gang sockets have the potential to draw 26A. To apply a departure you could not guarantee a lesser standard of safety is provided by using two one gang sockets.
Essex