Guest viewing limit reached
I am not sure if this is acceptable?
If I am using a 2 module enclosure for 2 MCBs both fed from a MCB in the main consumer unit. Would I have to use a busbar inside the 2 module enclosure or would it be ok to have a cable link at the bottom of the MCBs.
I have heard people say this is a nono inside a C/U, but my thinking in this example is that as long as the cable is rated high enough for the MCB from to C/U then there shouldn't be a problem as overcurrent protection is provided by the MCB feeding the 2 MCBs
Thanks Marcus
you should have a D/P switch in that unit in order to isolate. therforei suggest you buy one of these. I f fed from RCD on main CU, replace the sub . RCD witha D/P switch.
do it right
do it right
ah ok, so there is a requirement for double pole isolation, cool thanks
So if it was a metal 2 module enclosure (like the wylex one available at Screwfix) and it was earthed is that then not alright.
What is wrong with that? It should be earthed one way or another, either earth rod if TT or from the feed supply.
not sure there will be space for one of the BG garage c/u
How small is the garage?!
There will always be wall space, unless it is a doll's house!
So what is it for? Not enough slots in the CU?!
He has some underfloor heating in the kitchen of a kitchen-dinner, on its own B6 MCB he has added underfloor heating to the dinner part but its total load is just over 1500w so to much to add onto the B6 MCB. The cable for the kitchen underfloor heating is already in and very difficult to replace it is only 0.75 T&E so cant just swap the B6 MCB for a higher rating.
The consumer unit is full up, So a suggestion I said which might work, without ripping all of the plaster down. Was to swap the B6 for a B10 or B16 and then but an enclosure next to the C/U feed from the new MCB via new cable, then a B6 in the enclosure would protect the kitchen floor cable and a B10 for the dinner underfloor heating, on a thicker cable
Yes, you could use something like this:
But you would need to allow for earthing the metalwork (no idea if it has a terminal strip inside or not) and you could use Wago for joining the neutrals. Not ideal, but if that is all the space you have...
The preference for a bus-bar comes from a number of factors, reliability is one, the other is most MCB can only take 25mm total conductor, so you could not loop in and out cable for 100A as needed in a CU. But reliability/safety from a good connection is reason #1
That's going to be a problem then as that's non-compliant with the regulations, and if you disconnect it and reconnect to a new CU then you need to correct such a significant non compliance.
I see what you are saying,
Yes I was thinking the same wago for the neutrals.
That makes sense about busbar vs cable loops, although just has a thought which maybe is better is to take 2 bits of T&E from the B10 MCB inside the c/u so each MCB in the enclosure is feed from a separate cable
The enclosure you sent me is a plastic one, the metal version of the same thing has an earth terminal inside. Would I be able to use the plastic one, as is it only C/U that have to be metal ??
[automerge]1587503253[/automerge]
I see what your saying, as in the cable is non-compliant, I will have to get confirmation on what is there
Yes, well spotted if it is going in to the CU like that as regs have 1.5mm minimum for power.
Quick and dirty would be to put a double 13A socket on that heater breaker (upgraded to 16A) then you would be OK to connect 0.75mm round cable to it via a plug and 5A fuse, etc., and other heater on the other plug.
Buckinghamshire
Other
If other, please explain
Electrician for live events and touring temporary systems
2 module enclosure
marcuswareham,
pc1966,