Ring main.
Yes I have the regs book, which states final circuits should be connected to a seperate way in the CU. But I've seen so many others argue this is OK??
I'll reiterate, a circuit originates from an individual OCPD if some dipstick has decided to combine 2 RFCs into 1 circuit incorrectly then He / She needs to hang up their screwdrivers, and take up another Trade.
I've never seen many people argue that two ring finals one one MCB is a good idea.
I'm not saying it's correct just saying what I've seen. That's why I've asked the question to make sure its correct.
[automerge]1588089613[/automerge]
Thanks for the advice it is much appreciated?
Well no then it isn't
[automerge]1588089689[/automerge]
You are more than welcome Mate
[automerge]1588089831[/automerge]
See description of a circuit in OSG or BS 7671
You could put more than one radial on a MCB but its not good practice.
2 Rings on 32mcb is dangerous are you sure it's not 2 radials?
2 rings would have four wires goinging into a MCB
Some people spur off a MCB maybe it was that - 3 wires?
Definitely two rings there are 4 cables in the MCB. I'm going to add another way and seperate them.
Looking at this thread there is argument that it is safe but not common
_theiet.org/forums/forum/messageview.cfm?catid=205&threadid=32208
I suppose you could argue it's just extending the Ring??? - 2 large rings would surely cause constant tripping.
JKMRK1,
Risteard,