I'm just putting what the C&G book says but GN3 does also says "When testing the effectiveness of main equipotential bonding conductors, the resistance value between a service pipe or other extraneous-conductive-part and the main earthing terminal should be of the order of 0.05 ohm or less"
Source URL: SparkyNinja Webinars - https://www.electriciansforums.net/threads/sparkyninja-webinars.184880/

but with the Regs and OSG you can measure the length and do the Maths and generally you would be within 0.05
no problems with that statement, what is the query?
 
I think everyone is happy with "of the order of 0.05 ohm or less" as a reasonable test of stuff bonded with moderate cable lengths.

But not when it is turned in to the belief it must be less than 0.05 ohm!
 
I think everyone is happy with "of the order of 0.05 ohm or less" as a reasonable test of stuff bonded with moderate cable lengths.

But not when it is turned in to the belief it must be less than 0.05 ohm!
Install a larger main bonding conductor.
 
It's interesting, as a recently qualified electrician, this value was drilled into students.

Also, when I did 2391 it was seen as the value you cannot exceed.

I just assumed it could never be exceeded in any circumstance

And when you asked the tutors why it had to be 0.05 what did they give as the reason?

Or do you just blindly accept such things without seeking to understand the science behind it?
 
And when you asked the tutors why it had to be 0.05 what did they give as the reason?

Or do you just blindly accept such things without seeking to understand the science behind it?

I donr blindly accept anything. I asked the question.

It's not understanding the science behind the 0.05ohms threshold that is the main question here?

we are trying to determine how this figure is being treated.

I understand the science but I was still wrong in my understanding of what to do when this figure Is not satisfied.

That's what we are trying to accertain
 
maybe I'm wrong but on his latest video he talks again about taking prospective short circuit current at the end of a circuit and I don't think this is right? it's not the same as an earth fault if a fault starts drawing too much current then the device will trip even if it's a long way away PSCC is only need a the source.

Line and Neutral unlike CPC are the same size conductor.

If it was a long run with then there would be volt drop on both line and neutral, your not going to have a bigger Neutral than your Live are you.

edited sorry pscc
 
Last edited:
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
SparkyChick,
Last reply from
davesparks,
Replies
39
Views
5,457

Advert

Back
Top