I suggest you read the thread. Then tell me where I have complained. And I suggest @Taylortwocities keep his suggestions to himself.
All say a 16A appliance cannot be taken off a 32A ring because the regs say so, even though it can be done quite safely - and I have seen this done. Fine, I go with that, as we are all best going one way
I pointed out splitting the ring into two 16A radials, bringing up the point that a radial created out of the split may have 13A sockets on it, but a 16A commercial socket/plug can be fitted for a 16A appliance - unlike the Continent we do not have 16A sockets/plugs. I see no one took this one up.
You lucky girl, @Julie.
He must be good at something to distract you from the thrilling subjects of British standard numbers!
There is nothing to stop you splitting the ring, turning it into two separate 16A (or 20, if you like) radials and connecting your 16A appliance to this radial.I wrote this, which appears to conform with regs.
As I mentioned splitting the ring into two radials is an option. But this raises another flag. A 16A radial may have a number of 13A sockets in series on it. Either the 16A appliance can be hard wired into the radial, with cable outlet, or fit the commercial plug/socket.
Ripping a house to pieces to get in a cable for a 16A radial, when there is another simpler, and cheaper, way is rather well.....
Some sense at last.There is nothing to stop you splitting the ring, turning it into two separate 16A (or 20, if you like) radials and connecting your 16A appliance to this radial.
You do, of course, have to take note of the existing loads on the circuit. This is contained right at the very start of BS7671 under the jazzy title "Fundamental Principles".
That is what I asked and other way to around a problem.Unless I've missed something, it appears to apply to ring finals. With this in mind, what do other forum members feel about a 16A socket on a ring final, locally protected by a 16A breaker?
Interesting. So the installation I saw with a Wylex switch on the ring with a 16A fuse to a commercial socket outlet appears to fall in line with the regs, at least in part. Although, would a 16A commercial socket/plug comply or would it have to be permanently connected.Here is something that may be of interest to this thread. It's from the OSG, App. H2 -
Final circuits using socket-outlets complying with BS 1363-2 and fused connection units complying with BS 1363-4.
"A circuit breaker not exceeding 16A."Here is something that may be of interest to this thread. It's from the OSG, App. H2 -
Another great thread from this troll.
Asks for advice then won’t listen to it. This guy would try to argue that black is actually white.
What's the point of having a RFC on a16 Amp OCPD? just to accommodate a 16 Amp socket simpler to run the socket from a dedicated 16Amp circuitHere is something that may be of interest to this thread. It's from the OSG, App. H2 -
Hi Pete. The 16A breaker would be local protection rather than whole circuit protection. It would protect only the 16A socket, and the ring would be protected by the usual 32A breakerWhat's the point of having a RFC on a16 Amp OCPD? just to accommodate a 16 Amp socket simpler to run the socket from a dedicated 16Amp circuit