Hi Pete. The 16A breaker would be local protection rather than whole circuit protection. It would protect only the 16A socket, and the ring would be protected by the usual 32A breaker
Seems like there might be a market for some sort of premade unit that would comply with that to allow the 15A oven example to be connected (where diversity and other loading conditions allow). Doubt it would be pretty enough to be on show though....Hi Pete. The 16A breaker would be local protection rather than whole circuit protection. It would protect only the 16A socket, and the ring would be protected by the usual 32A breaker
There are small, cheap units available that would take MCBs such as this one from wylex:Seems like there might be a market for some sort of premade unit that would comply with that to allow the 15A oven example to be connected (where diversity and other loading conditions allow). Doubt it would be pretty enough to be on show though....
"16Amp socket from a rfc protected by a 16 Amp breakerWas what was said MateHi Pete. The 16A breaker would be local protection rather than whole circuit protection. It would protect only the 16A socket, and the ring would be protected by the usual 32A breaker
I think we may be at cross purposes Pete? Are you referring to someone else's post?"16Amp socket from a rfc protected by a 16 Amp breakerWas what was said Mate
or try B&Q. just use a choc block and 2 layers of insulating tape.Suggest you ask on another forum. The Screwfix one maybe has the sort of getting around the regs ‘advice’ that you are looking for.
I would stop short of saying a 16A fuse definitely complied, but I couldn't say that it didn't comply either. The 16A breaker is mentioned in the OSG (in the 17th edition too, so it's not a new thing), being an IET publication we can assume it carries some weight.Interesting. So the installation I saw with a Wylex switch on the ring with a 16A fuse to a commercial socket outlet appears to fall in line with the regs, at least in part. Although, would a 16A commercial socket/plug comply or would it have to be permanently connected.
It looks like the rule of thumb that not higher that 13A off a ring is not true.
Yes Sorry Mate ignoreI think we may be at cross purposes Pete? Are you referring to someone else's post?
That may not always be practical - such as ripping a house apart for one cable, or no spare slot in the CU.What's the point of having a RFC on a16 Amp OCPD? just to accommodate a 16 Amp socket simpler to run the socket from a dedicated 16Amp circuit
That indicates it does comply, but the appliance has to be permanently connected, not via a disconnecting device of any sort (a socket that is commercial or domestic). The picture you posted in your first post does state so.I would stop short of saying a 16A fuse definitely complied, but I couldn't say that it didn't comply either. The 16A breaker is mentioned in the OSG (in the 17th edition too, so it's not a new thing), being an IET publication we can assume it carries some weight.
Without meaning to come over as pedantic, it specifically states a 13A fuse or 16A MCB.c) with a 16A fuse.
I am not planning anything. There are lots of general continental appliances that draw more than 13A. This must be a common occurrence.Out of interest, what do you plan to use the 16A socket for?