Guest viewing is limited
Hi Pete. The 16A breaker would be local protection rather than whole circuit protection. It would protect only the 16A socket, and the ring would be protected by the usual 32A breaker
Seems like there might be a market for some sort of premade unit that would comply with that to allow the 15A oven example to be connected (where diversity and other loading conditions allow). Doubt it would be pretty enough to be on show though....
 
Seems like there might be a market for some sort of premade unit that would comply with that to allow the 15A oven example to be connected (where diversity and other loading conditions allow). Doubt it would be pretty enough to be on show though....
There are small, cheap units available that would take MCBs such as this one from wylex:


You would have to decide if a plastic one was ok, or if a metal one would be more appropriate. But yeah, you'd want it hidden in a cupboard out of view!
[automerge]1600196972[/automerge]
Personally, I think a 16A socket on a ring final, locally protected by a 16A MCB may be safe, and may be compliant.

Here is a comparison of the time/current characteristics for a 13A BS1362 fuse vs. a 16A BS60898 MCB. Appologies for the poor quality of the image, but hopefully you can see that for most of the curve, the 16A breaker opens quicker for the same overcurrent.

13A BS1362 vs 16A BS60898.jpg
 
Last edited:
Hi Pete. The 16A breaker would be local protection rather than whole circuit protection. It would protect only the 16A socket, and the ring would be protected by the usual 32A breaker
"16Amp socket from a rfc protected by a 16 Amp breakerWas what was said Mate
 
Interesting. So the installation I saw with a Wylex switch on the ring with a 16A fuse to a commercial socket outlet appears to fall in line with the regs, at least in part. Although, would a 16A commercial socket/plug comply or would it have to be permanently connected.

It looks like the rule of thumb that not higher that 13A off a ring is not true.
I would stop short of saying a 16A fuse definitely complied, but I couldn't say that it didn't comply either. The 16A breaker is mentioned in the OSG (in the 17th edition too, so it's not a new thing), being an IET publication we can assume it carries some weight.

The actual regulations concerning ring finals are surprisingly sparse. The design guide in app 15 will ensure compliance, but is not actual regulation, and deviation from it doesn't automatically mean non compliance.

A double socket is designed to run at 20A, so yes, it is expected that a load of greater than 13A will be placed at a point on the ring for at least some of the time.
 
[automerge]1600242694[/automerge]
What's the point of having a RFC on a16 Amp OCPD? just to accommodate a 16 Amp socket simpler to run the socket from a dedicated 16Amp circuit
That may not always be practical - such as ripping a house apart for one cable, or no spare slot in the CU.
 
Last edited by a moderator:
I can't answer 'how I get around the problem' because I've never encountered it, but it's an interesting theoretical question.

It might be acceptable for a 16A point load to be applied to a 32A RFC, especially if the diversity applicable or the manner of operation of a permanently-installed appliance can be foreseen and factored in. An oven that requires an average of 15A for a few minutes and then drops back to below 13A average, is not much different from one with a smaller element that draws 12A solidly for a longer warm-up time (It is different, though, because the heating in the circuit cables is proportional to I² but the heating in the oven is proportional only to I.)

We must distinguish between three possible kinds of problem arising from a large fixed load on a general-purpose RFC:

1) Risk of overloading cables, since on a 32A RFC conventionally In>Iz. Normally, this does not happen. If it does, it's very minor, which is why houses don't burn down when RFCs get broken near one end.

2) The load accounts for too great a fraction of Ib to allow the circuit to fulfil its role of supplying general purpose socket outlets. This is not specific to RFCs, it is a simple diversity conflict, that would occur equally on a 32A radial S/O circuit. If the circuit is intended to provide a useful amount of power elsewhere, a 32A circuit with a 16A load is probably better than two 20A circuits with a 16A load on one of them. The bigger the circuit, the better diversity works.

3) The accessories are not suitable for a 16A load. This is simply a practical consideration that is easily overcome by careful selection of equipment.

My view is that it is bad practice to burden a general-purpose socket-outlet circuit with large single loads unless their duty-cycle is known to be modest. I think this is actually a more significant consideration than the point loading of an RFC affecting current distribution.
 
I would stop short of saying a 16A fuse definitely complied, but I couldn't say that it didn't comply either. The 16A breaker is mentioned in the OSG (in the 17th edition too, so it's not a new thing), being an IET publication we can assume it carries some weight.
That indicates it does comply, but the appliance has to be permanently connected, not via a disconnecting device of any sort (a socket that is commercial or domestic). The picture you posted in your first post does state so.

But as other have noted, a look at the ring and its loading, it essential.

It was noted in previous posts that a 16A radial can have a 16A commercial socket directly off it giving a disconnection device.

I also noted in a previous post, that changing a 32A mcb for a 16A on a ring gives the same result, in that a commercial socket can be fitted directly onto the 16A ring. Of course the loading of the ring would need to be assessed, as per normal. I know my 32A ring could be dropped to 16A without any problems, as little is taken off it - TV, lap top, phone chargers and the occasional vacuum cleaner.

So, as been gleened so far:

1) A 32A ring can have a 16A appliance off it, with the appliance:
a) only being fixed;
b) with an isolation switch;
c) with a 16A fuse.

2) A 16A radial can have a 16A appliance off it with a fixed appliance or off a 16A commercial socket (the only 16A sockets available in the UK).

3) A 32A ring can be re assigned to 16A ring by a mere change of an mcb/rcbo. The appliance can be fixed or with a 16A commercial socket. As per the 16A radial.

Any constructive comments?
 
I would not connect a 16A load to a 16A general-purpose domestic socket-outlet circuit. When the 16A load is in operation at full current there is zero remaining capacity for other appliances, and when it drops back in duty-cycle there might be only a few amps. Since one would expect at least some load on such a circuit, small overloads might occur frequently that probably would not trip the MCB. This is an unsatisfactory situation that should be avoided to prevent premature failure.
There is no need to protect the circuit at 16A if the cables are installed with an Iz>20A which is a requirement of them being suitable for a 32A ring. Therefore it could be protected at 20A. Personally, I would rather it be protected at 32A.

c) with a 16A fuse.
Without meaning to come over as pedantic, it specifically states a 13A fuse or 16A MCB.

Note, I am not endorsing this as a 'good idea' (tm). There is a recommendation to connect loads of this size to dedicated circuits, which I think is sensible. But it does seem that a permanently-installed load that can operate correctly from a B16, that probably has a long-term cyclic consumption of less than 13A, may be connected to a 32A RFC if overall expected loading permits. As above, I don't like the 16A OCPD option.
 
Lucien,

A dedicated radial supply is the best of course, but I did not want to state the obvious. Just the options other options.

So, a 13A fuse or a 16A mcb

Yes, a 20A radial or ring gives a margin of wiggle room when a 16A appliance is connected.
[automerge]1600371415[/automerge]
Out of interest, what do you plan to use the 16A socket for?
I am not planning anything. There are lots of general continental appliances that draw more than 13A. This must be a common occurrence.

Apart from running a new cable back to a CU, which may be very expensive and impractical (the lady of the house would not be amused if her nice house is ripped up), other approaches can be looked at. And as this thread has brought to light easier solutions are available and within current regs.
 
Last edited:
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

John-SJW

Deleted account
Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Manufacturer / Distributor / Supplier / Inventor - etc

Thread Information

Title
16A off 32A ring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
54
Unsolved
--

Advert

Thread statistics

Created
John-SJW,
Last reply from
westward10,
Replies
54
Views
11,982

Advert

Back
Top