Always wondered what the red button was for. ?
I'm pretty sure that's what is on my 50m cable reel, certainly not an RCD, I think its old enough that RCD's where not available back then.To be fair a lot of the red buttons are just overload reset buttons.
13A fuses have Zs limit of 2.3 ohms (Table 41.2) so assuming your supply Zs is around 1 ohm at the socket then if your cable R1+R2 is 1.3 ohm or less no problem?
Not as such.They do give specific limits on length in the ISITEE code of practice though.
Not as such.
They recommend max lengths of 12/15m for 1.25/1.5mm CSA in section 10.10, and also that longer leads should have RCD protection but that might be part of the installation.
However, 15m of 1.5mm is only 0.36 ohm R1+R2 (from OSG Table I1) so well short of any limit on OCPD disconnection.
Where is 'table 15.4' located?But surely table 15.4 must be followed. And extension are tested as non fixed equipment, ie. separately to the installation.
It is a little shorter, works out at 13.5m of 1.5mm flex, not allowing for plug/socket resistance (which ought to be very small).We have a rule of thumb that where the earth bond exceeds 0.18 ohm (I believe this equates to the suggested lengths in the CoP) that it is recommended it is only used with 30ma rcd protection
Actually if using the resistance from OSG it is about 15mIt is a little shorter, works out at 13.5m of 1.5mm flex, not allowing for plug/socket resistance (which ought to be very