clanky
-
Thanks to being quarantine for a week i finally managed to have a go at the the practice exams in the course and i have a few questions for the more knowledgeable of you as im wasnt entirely sure of the correct method to get to the right answer. Thanks for any help in advance:
‘how is the nominal voltage at origin of an installation determined?’
I thought the answer was in the start of paragraph 313.1 and is quoted as ‘..calculation, measurement, enquiry or inspection.’ but the answer in the exam was enquiry only?
‘radial power circuit rated at 16A has been installed on a TT system what is the max. disconnection time for the AC circuit?
The correct answer in the exam is given as 0.2s but (using the table 41.1) I was confused as that assumes the supply is between 120 and 230v. I know its unlikely but for 50 to 120v the time is 0.3s. Which is obviously more. Am I missing something?
What is the condition of external influence in which an installation supplied from a low voltage network incorporating overhead lines would not normally require additional protection against overvoltages of atmospheric origin.
I struggled to find anything in the body of the main text for this one so I just used the table listing AQ1 as ‘normal’ Although I got the question right, I felt like I was just making an educated guess. Is there anything im missing?
Apologies for being a pendant but i have plenty of time before i have an opportunity to sit the real exam so i may as well use it usefully.
‘how is the nominal voltage at origin of an installation determined?’
I thought the answer was in the start of paragraph 313.1 and is quoted as ‘..calculation, measurement, enquiry or inspection.’ but the answer in the exam was enquiry only?
‘radial power circuit rated at 16A has been installed on a TT system what is the max. disconnection time for the AC circuit?
The correct answer in the exam is given as 0.2s but (using the table 41.1) I was confused as that assumes the supply is between 120 and 230v. I know its unlikely but for 50 to 120v the time is 0.3s. Which is obviously more. Am I missing something?
What is the condition of external influence in which an installation supplied from a low voltage network incorporating overhead lines would not normally require additional protection against overvoltages of atmospheric origin.
I struggled to find anything in the body of the main text for this one so I just used the table listing AQ1 as ‘normal’ Although I got the question right, I felt like I was just making an educated guess. Is there anything im missing?
Apologies for being a pendant but i have plenty of time before i have an opportunity to sit the real exam so i may as well use it usefully.