Says ir is high on sockets what is that all about?
so i have finally received the EICR report today. So there are only 5 off C2 findings.
One is the distance of the consumer unit from the waste pipe.
C2 "consumer to near waste pipe " << is all he has written on the report.
I say that and figured ir = Insulation resistance, guess not?Says ir is high on sockets what is that all about?
Code 1 is he could not find earthing rod from consumer unit.Item 2 - nonsense
Item 3 - if out of the zones nonsense however they may not be suitable for the environment
Item 4 - no idea what that means
Item 5 - probably no continuity on r2 so that's okay
Item 6 - no idea what that means
As above what is the Code 1?
Description Quantity Unit Price (£) VAT (%) VAT (£) Total (£)
1 bathroom lights and extractor fan repair
2 sockets - repair investigate fault and repair
3 lounge lights installation
4 ring sockets on earthing fault
5 oil new bonding supply
6 fuseboard installation, relocation fuseboard & new tt ststem
so planning to so all the remedial work. Not with him. He want £1,700 for everything, which seems high. Going to replace the consumer unit, just not relocate it.
I am an engineer. but not an electrical engineer. I think he has been evasive, to ensure he gets the work. I wouldnt touch him with abarge pole.The report is nonsense and he does not know what he is doing. The installation could be fine , may not be, may not be and have nothing to do with what he has 'garbled out'.
I have been inspecting for a long time and what you have SIr is not uncommon and quite a disgusting stain on this industry I love and have pride in.
The inspection is conducted against the current edition of BS7671 if it complies with BS 7671 there would be no C2 codings; that and it cannot be satisfactory with C1, C2 or F.I.
As for the wording on those codes - oh dear!
I could go through them all, subjective nonsense, example point 6. What reading is high? What does he mean by 'high'?
What is the C1 ? - what was done at the time of the inspection to make this C1 safe?
I certainly would be very concened about letting this person touch the installation
Can I ask if you have any electrical experience / background? You seem to have some insights.
1.3 Condition of distributor's earthing arrangement C1The observations don't include the Code 1 and multiple Code 3s on the inspection schedule.
Just very quickly looked and stunnedReport attached.
Utter Garbage!Report attached.
They were broken by last tenant. so going to replace them.They should be itemised in Section K.
What is wrong with the lounge lights it makes no mention of those.
Reply to the thread, titled "Existing Consumer Unit close to vertical waste pipe" which is posted in UK Electrical Forum on Electricians Forums.