Guest viewing limit reached
Sure this has come up before but yesterday testing after adding a spur and end to end readings on CPC come out about 0.2ohm over expected reading (was expecting about 1ohm from LL & NN (0.65)
Checked all sockets I could see (some were very old so suspect the sockets themselves might be a contributing factor) other possibility is JB under floor.
Question is would you just report this on meiw, start ripping up floorboards, recommend FI or what?
Earthing system was TT. Zs - 9.75ohms
Also there was quite a bit of original stranded copper in the circuit.
That was one thought. Didn't actually spot it myself but obviously that would make sense. There was a fair bit of stranded 2.5mm but think the CPC was 1.5 in that.
Either way, what is best way to approach to meiw cert.
Newcastle-under-Lyme
Other
If other, please explain
Possible trainee
Marginally high CPC end to end readings