Hi,

I've recently looked at a fault with an intermittently tripping RCD at a property for a landlord I do the odd job for.
Got there and did the basics, IR'd the cables, looked at resistances across the pump, got acceptable results everywhere I looked. Played with the heating, demanded hot water and central heating to try and recreate the fault. Absolutely nothing. Apparently it is very sporadic and can be days apart, which given the time of year means the heating does not trigger it every time..

The CU wasn't split sensibly to my mind with up and downstairs lighting and smokes on one RCD and heating, ring and oven on the other, I swapped the heating with one of the lighting circuits, to see if the fault moved, to give a slightly better split, and to be sure it wasn't due to some sort of cumulative high leakage from things plugged into the ring.

The fault has indeed followed the heating across to the other side of the CU. I am happy to admit I'm competent with domestic heating, but it's not my bread and butter, and am now scratching my head, mostly due to acceptable test results and the lack of repeatability.

It's a small 2 bed property with a Y plan set up.

Any thoughts would be much appreciated.

Thanks.
 
Did you test the mid position valve whilst moving the lever, I have had them fail IR testing in a certain position before, so weren't easy to diagnose.
 
Did you test the mid position valve whilst moving the lever, I have had them fail IR testing in a certain position before, so weren't easy to diagnose
Did you IR the equipment? L+N to E at 250V?
I did not, I did at from the CU, but as mentioned above I need to go and IR the kit while manually shifting the valve about.

I'll go and do this when I return to swap out the meter box hinges that have failed and report back. Seems like an incredibly obvious thing to check now :confused:
 
Update.
Went back today as it was popping the other RCD post move, again intermittently with no real pattern. Typically overnight but not every day.

IR'd the valve throughout the range and everything was fine, pump fine, stat. wiring all fine too. Upon pulling the god awful rats nest all the way out of the wall behind the controller (no box, nothing just connector blocks and shoved into the stud...) the room stat has a pre-heater in it which the neutral at the control end was either never connected, or not put into in the connector block properly, but eventually pulled this out of the wall hanging around bare copper ended. There was no obvious short to earth when testing this, but this is the only thing I can find as a cause. Now put away safely (or as safely as it can be under the circumstances!). Back to waiting, if it still pops I'm now at a loss.
 

Reply to the thread, titled "Intermittent central heating fault.." which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top