Our company just installed fire alarm system into garden centre warehouse,problems with alarms going into fire state.Smokes installed on ceilin purlins,it seems that the centre sprays the plants/flowers with water,hence a damp humid atsmosphere,any suggestions to fix this frustrating problem cheers.
 
Put heat throughout - but thinking it will take alot of heat to set these off - with the big space

Put the smoke alarms higher up so the spray has more room to disappear before it hits the alarms

Other option is work out the risk areas and miss the locations which the spray is activating the alarms - I dont know the layout, but a flat internal roof is an advantage as the smoke spreads across the top of the roof setting smoke detectors a few meters away off.

If you have peaks then you need smokes in each peak.

Pictures of the location would be a great benefit!
Different situations different options with fire alarm systems
 
What make of kit have you installed???

Special marine environment detctors are aviailable from most manufacturers for situations like this one


Your risk assessment of the area should have highlighted this.:wink:
 
twists in it all if your in expierienced..

sorry for jumping in , hi lenny or any other artful electrical dodger, im looking at a drawing and they have put two smoke alarms in the same hall way,

isnt it a smoke alarm shouldnt be more than 5m from any bedroom (domestic)???
 
What make of kit have you installed???

Special marine environment detctors are aviailable from most manufacturers for situations like this one


Your risk assessment of the area should have highlighted this.:wink:

All done to spec,problem not thought of at start,google marine detectors c what comes up cheers 4 advice
 
Would suggest beam detection in open warehouse situations, they are more controllable and more cost effective than smoke sensors. They work on the method of percentage of obstruction in air, and can be calibrated to suit different evoiroments. ie 30%, 40% or 50% set to activate fire, wher 100% will always activate fault. Fire Beam is possible the best on the market. At around £250 covering upto 100m x 14m its a bit cheaper than installing 20 optical smokes with cabling and labour.
Hope this helps
 
just looking at my drawing, the architect has said smoke alarms to be on deticated ciruit and before rcd, but have seen some posts saying smokes and heat on rcd is fine.....
 
Bit old school to ask for fire circuit to be before rcd, would suggest asking him the question in a RFI. Normal standard is to follow wiring regs, with dedicated MCB or RBO for the fire alarm panel, and wired in enhanced fire proof cable to a lockable switched double pole fused spur adjacent to control panel. This way you are covering both regs.
 
i ve had a smilllar problem in a big warehouse where there were misters to keep dust down which was setting off detectors we changed them to heat still had problems mist/water causing shorts on system and setting devices into fire due to when the voltage drops to a certain range it goes into fire thia is done in normal circumstances by there being a 470 ohm resistor or a zenner diode built into the smoke or heat detectors being put across the head once the optical head being set off or the thermister in the heat detctor being activated. anyway we eneded up using linear heat trace cable being used not ideal but done the trick
 
id go for ror heats,if smokes are being set off beams will too if the steam is causing the problem.you could go down the vesda route but will mean ripping the system out and starting again,no doubt at your company's expence
 
I take your firm didn't do the design for the Fire Alarm circuit

If the design company specified what you should put in and you did it to spec then sorry your job is done -if it does not work because of a problem with the wrong equipment in the spec (from the sound of it this is the case) the design company is responsible.

Throw it back at them and tell them to redesign it as their system is not working to the customers spec and it is not fit for purpose!

Then if they change the system they are responsible for meeting the costs encored, if they dont pay up then that's a claim against their PI.


As this post is now a few days old have you sorted it yet?
 
Vesda, or airsense can be a problem in this situation, water evapourators can help, but the filters dont really like water.
Beams are the only answer in hostile situations.
As to public forums, I would like to think i joined to help others
 
Vesda, or airsense can be a problem in this situation, water evapourators can help, but the filters dont really like water.
Beams are the only answer in hostile situations.
As to public forums, I would like to think i joined to help others

steam is not a problem for vesda and the small amount of steam which could arise in this situation would pose no problems at all.most ir beam manufactures say not suitable for areas of dust and steam..
 
Alarm man, see were your coming from, with the amount of steam or water when it condistates, but would wonder how much a vesda or airsense could function over a long period in such evoroments, and to what extent. The old fixed beams being a pain in the rear have now been sorted with programmable beams such as Fire beam made by my old company Lemtronics. In areas of dust or high combustion would certainly go for the fast response of vesda.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
-
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Fire
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
cliffed,
Last reply from
Guitarist,
Replies
17
Views
2,381

Advert

TrueNAS JBOD Storage Server

Back
Top