graham123

if you have plastic pipes feeding a mixer shower unit, does the micer shower unit need supp bonding?
 
So because i get a reading above 1667 ohms, the mixer tap does require a supplemetarty bond to the electrical circuits in the room
 
Have sorted it now, so, insulation resistance test between the cpc at light fitting and the mixer tap was >999 so its just a metal part and does not require a supplementary bond. Now in an EICR their is no 30ma RCD protection in the bathroom. So am i right in saying C3 as their is no extraneous conductive parts?
 
Have sorted it now, so, insulation resistance test between the cpc at light fitting and the mixer tap was >999 so its just a metal part and does not require a supplementary bond. Now in an EICR their is no 30ma RCD protection in the bathroom. So am i right in saying C3 as their is no extraneous conductive parts?

Confused? So your doing a EICR but don't know how to test for supplementary bonding? I would question your competency level! Sorry
 
Last edited:
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Supp Bonding
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
27

Thread Tags

Tags Tags
bonding

Advert

Thread statistics

Created
graham123,
Last reply from
Geordie Spark,
Replies
27
Views
3,332

Advert

TrueNAS JBOD Storage Server

Back
Top