  1. S

    Collective thoughts about issue… Pub kitchen

    I would definitely change to 16 A Commando sockets with Isolators. Fixed load so short circuit protection only required. Swap the RCBO for a 32 Amp and make sure it's a "Type A" tripping characteristic. Not surprised it keeps tripping. I would put an a clip on ammeter on the cable, I think you...
  2. S

    UK First visit , Bungalow question.

    If you are rewiring don't just do the usual 2.5mm for power circuits. Try to keep the cables out of the insulation. You will probably still need to wire in 4.mm to satisfy thermal constraint. Hope this is helpful.
  3. S

    UK First visit , Bungalow question.

    Best "Magic" one in then.
  4. S

    3 phase EV Charger on 2 phases.

    I will let you know what Porsche say (if I get a reply)
  5. S

    3 phase EV Charger on 2 phases.

    The answer will come from Vehicle Manufacturer's. If they are brave enough to commit !
  6. S

    3 phase EV Charger on 2 phases.

    Thank you for your reply Simon, good point about the DNO and 3 phase supply. I will ask my Customer to follow this up. Although not correct and will still imbalance the neutral, the incoming cable is 3 core CNE. They have tapped off one of the phases twice on the main feeder cable outside of...
  7. S

    3 phase EV Charger on 2 phases.

    Hi all, I have a site where the network cable was damaged do DNO has provided 3no. 100 Amp Fuses. 1 Fuse on L1, 2 Fuses on L2. L3 is damaged in the road and not in service. I have looked at onboard charger diagrams of several vehicles. As far as I can make out the "3-phase" capable vehicles have...
  8. S

    open PEN protection.

    Would any fellow electricians consider using an open PEN device to protect a metal trailer used as a "Canteen". It is likely to be often connected to TNCS (forbidden by 717.411.4) and placed on concrete which makes the use of TT and rod impossible. I can draw similarity to an EV charge point...
  9. S

    Tesla wall charger load curtailment

    https://matt-e.co.uk/wp-content/uploads/2023/04/SP-ECVP-R-Cxx.pdf Tesla load curtailment solution
  10. S

    Tesla wall charger load curtailment

    Matte-e make a open pen device which also includes monitoring of the incoming supply I believe. Just learning myself !
  11. S

    Dodgy trade pictures for your amusement! - 1 Million Views!

    Buried in the Lounge wall, neutral continuity fault on Ring Circuit, found it with a Fluke cable tracker, couldn't believe how accurate it was. The...
  12. S

    Dodgy trade pictures for your amusement! - 1 Million Views!

    Don't put the junction boxes in the wall cavity it makes fault finding really hard - Builders again.
  13. S

    Dodgy trade pictures for your amusement! - 1 Million Views!

    Open ended cable chucked under the office floor tile, they could've at least turned the Isolator Off !