Hi,
Ok, so see the consumer unit below, this happens to be one I fitted, but anyway...
I am going to be moving house soon and am going to replace the CU thats in the house with one of these Hager boards, exactly the same.
I want to put the security alarm and a supply to my secure store room, and roller gagage door on their own RCBO's...
Is this a stupid question but where would you connect the supply neutral to the RCBO too exactly? I know with the MK boards they give you space on a main neutral bar, but this doesn't have one.
Am i right in thinking I need some extra bits for the rail at the top?
I never fit RCBO's hence the question, I have probably only ever fitted 3 in my life, I know how they connect but just wondered what you would do with this board?
Thanks,