I was asked to test five caravan pitches for someone I've done a few jobs for. Now, I'll admit my knowledge on TT systems is not vast so I'm looking for a bit of advice. The install has been tested by a large local contractor every three years. When I got there the setup was as follows. BS 1361 cutout - meter- 63 amp 100mA rcd - 16mm Swa - 5 way db (63amp 30mA main switch) (roughly 20m away),then out to the hookups via 10 amp mcb's. There was a 10mm earth out to multiple rods connected to the RCD steel enclosure (as told by customer). There was also a 16mm earth to the PME cutout? I know this is incorrect so I disconnected it and got 110 ohms Ra. This is obviously classed as stable but not ideal. My problem is, why did this other contractor not pick up on this, or am I the one that's wrong?? Before anyone else pipes up I know there are other faults ie no overload protection on the supply to the 5 way db!
Thanks for reading!
 
Tourers definately every year, I haven't got the BGB with me to confirm 3 years with statics, however ,most holiday parks would have a condition report of the vans every year for insurance reasons I suspect regardless of the regs, it is cheaper insurance if the vans checked annually.
 
Statics every 3 years, tourers every year. That's what it used to be, but I've been away from the game for a few years-has it now changed?

Yes, 3 years for statics, therefore OP's site may well be a static caravan site as stated every 3 years. Depending on the actual static van tn-s is allowed, not to sure about PME though.
 
Yes, 3 years for statics, therefore OP's site may well be a static caravan site as stated every 3 years. Depending on the actual static van tn-s is allowed, not to sure about PME though.
Don't think it is an issue, TNS the better way, that said without the BGB were all guessing, Murdoch is on now, if he sees this he may put us out of our misery.
 
If residential site, TN-S can be used for direct connection to caravan. TN-C-S can also be used as long as not metal clad units. OP are the static vans metal clad? This could be why previous EICR are satisfactory.
 
[ElectriciansForums.net] Caravan hookupsFound this , hope it helps
 
Personally I wouldn't use isolated rods at each hookup.
I'd be looking to create one large earth nest to give the lowest most stable Ra possible, possibly installing rods at each hookup but having them all linked together.

I know it would technically be a departure but I see no issue with having an earth nest of very low Ra connected to the MET and having the PME connected.
 
Personally I wouldn't use isolated rods at each hookup.
I'd be looking to create one large earth nest to give the lowest most stable Ra possible, possibly installing rods at each hookup but having them all linked together.

I know it would technically be a departure
but I see no issue with having an earth nest of very low Ra connected to the MET and having the PME connected.

That would be by far the best solution.

Why would you call it a departure?? All you are doing is providing an addition local N-E to the PME supply earth system. In this instance though, the Ra of the earth nest needs to be below 10 ohms, which isn't a very difficult task if you are installing a earth nest!!
 
Personally I wouldn't use isolated rods at each hookup.
I'd be looking to create one large earth nest to give the lowest most stable Ra possible, possibly installing rods at each hookup but having them all linked together.

I know it would technically be a departure but I see no issue with having an earth nest of very low Ra connected to the MET and having the PME connected.
That's all fair and well saying that, but it's going to be a much bigger and more expensive job to do it that way. I doubt they'll even do any of the recommendations!
 
A departure because bs767 1 says you must not have PME connected to the caravan pitches. But with the earth nest connected I see no reason why you shouldn't have PME connected,



Sorry, i didn't quite understand that you meant connecting the PME to the caravan. I thought you were only talking about PME up to the pitch hook-up cabinet, which is fine. Personally i wouldn't connect the PME through to the caravan, too much responsibility if something did go wrong no matter how good the TT earthing on the PME was....
 
Last edited by a moderator:

Reply to Caravan hookups in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top