just visited a customer who requires a 7.3kw hob connected to replace existing gas hob. Currently has a 2.3kw single oven connected to a 4mm T+E cooker radial (ref method c) Protected by a 32amp MCB

i advised that for the hob to be installed the cooker radial would have to be rewired using 6mm T+E as the 4mm was undersized for the load. but having done the calculations and thought about it I'm not quite sure any thoughts.

7.3kw + 2.3kw = Toal Max Load of 9.6KW = 41.7amps

Diversity applied(no socket at cooker switch) 10A + 30% remainder 10+9.51 = 19.51

with diversity applied Ib <In<It

can't find any reference in the regs to a 4mm cooker radial protected via 32amp MCB as the standard is 6mm/32mcb. Not standard circuit arrangement but as 4mmT+E can carry 37 Amps (ref C) I'm thinking that the additional load may be added.
 
Last edited:
yes 4mm is 37 amps ref method c (clipped direct) As i thought, 6mm may not be required as the calculations show that the existing 4mm cable is protected and can carry the load (diversity applied) no real difference to a 6mm cable being able to feed 15kw.

i just thought or assumed that 6mm was the minimum cable size allowed for a hob/oven appears i was wrong
 
Last edited:
i was just unsure about the 4mm cable size for a cooker radial. for some reason thought there was a minimum of 6mm. but the cable calcs prove there shouldn't be any problem with a 4mm on a 32amp mob with the required loading
 
A good question to ask is, do you understand why this will be okay, and why the diversity calculation allows for it....?

The diversity calculation allows for it because the hob and its elements will not be drawing the stated power ratings at all times and the same goes for the single oven. therefore the actual current draw with diversity applied is much lower than the stated max power ratings of both appliances. (10amps +30% of remainder +5amps(if socket on CCU) the formula used to calculate diversity. therefore a 4mm cable which can safely carry 37amps (ref method c) protected by a 32amp MCB
satisfys ib<in<It when diversity is applied.

as i posted earlier the standard circuit of 6mm t+e on a 32 amp MCB can supply up to 15kw load applying diversity of course. on reflection the situation described in my first post is no different electrically. i just assumed wrongly that it had to be a 6mm cable as a matter of course.
 
will be fine on 4mm. one reason 6mm is more otfen used is that you're more likely to have some on the van.

I would hazard a guess that most don't understand how to do the calculations and just work on a 1.5 = 6/10A. 2.5 radial = 16/20A. 2.5 ring = 32A. Cooker = 6mm & 40A.

4mm radial. Your pulling my leg. No such thing.

Well done IP007 for working it out for yourself.
 
Just thought I'd throw this one in.

once got involved in a lengthy debate with several sparks over diversity in oven/hob.

2 were adamant that you use diversity for the breaker size but not the cable size.

another 2 were adamant that you use diversity for breaker and cable size.

since this debate I've been asking other sparkles there opinions and the answers I get are one or the other or in one case I got "just use 6mm"

me. Well I always thought it was for cable as well as breaker, but not to sure now. As a result I have since erred on the side of caution and used cable suitable for full load without diversity and the breaker with diversity. If anything I have future proofed it.

i cannot pin it down in the regs as it depends on interpretation.

can anyone clarify.
 
Just thought I'd throw this one in.

once got involved in a lengthy debate with several sparks over diversity in oven/hob.

2 were adamant that you use diversity for the breaker size but not the cable size.

another 2 were adamant that you use diversity for breaker and cable size.

since this debate I've been asking other sparkles there opinions and the answers I get are one or the other or in one case I got "just use 6mm"

me. Well I always thought it was for cable as well as breaker, but not to sure now. As a result I have since erred on the side of caution and used cable suitable for full load without diversity and the breaker with diversity. If anything I have future proofed it.

i cannot pin it down in the regs as it depends on interpretation.

can anyone clarify.

Diversity will guide you towards the cable size. Then the MCB will be guided by the cable size.
 
you,us diversity to calculate the load current. from that you select a suitable cable size, using installation method and volt drop calcs. then you select your OCPD according to Ib<In<Iz. simplessssss.
 
I would hazard a guess that most don't understand how to do the calculations and just work on a 1.5 = 6/10A. 2.5 radial = 16/20A. 2.5 ring = 32A. Cooker = 6mm & 40A.

4mm radial. Your pulling my leg. No such thing.

Well done IP007 for working it out for yourself.

Well................he has been a member for 3 years... rather more than 3 weeks.
 
Yes. And I was happy to see that. Fantastic. My other comment was about others not the OP. I think what the OP done was great. I don't understand.
never mind. understanding with age you will get. [ElectriciansForums.net] 4 mm Cooker circuit 32amp MCB
 

Reply to 4 mm Cooker circuit 32amp MCB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I would put this down to 433.3.1(ii) - no overload protection needed because the load at the single socket can't overload the cable, being fused...
Replies
14
Views
1K
  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N
I’m not aware of any difference in diversity calcs based on circuit type. It’s done by appliance. Since a cooker circuit IS a radial anyways...
Replies
3
Views
4K
I suspect that’s because we are told at college, or certainly at mine, that diversity applies to the DB and overall installation for working out...
Replies
15
Views
5K
Hi - if I’ve looked up the right one, on page 10 (the electrical connection notes) it does say a 32A mcb is to be used, just saying.
Replies
12
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks