just visited a customer who requires a 7.3kw hob connected to replace existing gas hob. Currently has a 2.3kw single oven connected to a 4mm T+E cooker radial (ref method c) Protected by a 32amp MCB

i advised that for the hob to be installed the cooker radial would have to be rewired using 6mm T+E as the 4mm was undersized for the load. but having done the calculations and thought about it I'm not quite sure any thoughts.

7.3kw + 2.3kw = Toal Max Load of 9.6KW = 41.7amps

Diversity applied(no socket at cooker switch) 10A + 30% remainder 10+9.51 = 19.51

with diversity applied Ib <In<It

can't find any reference in the regs to a 4mm cooker radial protected via 32amp MCB as the standard is 6mm/32mcb. Not standard circuit arrangement but as 4mmT+E can carry 37 Amps (ref C) I'm thinking that the additional load may be added.
 
Last edited:
I would hazard a guess that most don't understand how to do the calculations and just work on a 1.5 = 6/10A. 2.5 radial = 16/20A. 2.5 ring = 32A. Cooker = 6mm & 40A.

4mm radial. Your pulling my leg. No such thing.

Well done IP007 for working it out for yourself.

Well................he has been a member for 3 years... rather more than 3 weeks.
 
Yes. And I was happy to see that. Fantastic. My other comment was about others not the OP. I think what the OP done was great. I don't understand.
never mind. understanding with age you will get. [ElectriciansForums.net] 4 mm Cooker circuit 32amp MCB
 
I'd have to say thanks too. :stooge_curly:
I've been told it's calculate the design current, select the protective device rating, then the cable ?
as long as you get the same answer.
 

Reply to 4 mm Cooker circuit 32amp MCB in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I would put this down to 433.3.1(ii) - no overload protection needed because the load at the single socket can't overload the cable, being fused...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top