just visited a customer who requires a 7.3kw hob connected to replace existing gas hob. Currently has a 2.3kw single oven connected to a 4mm T+E cooker radial (ref method c) Protected by a 32amp MCB
i advised that for the hob to be installed the cooker radial would have to be rewired using 6mm T+E as the 4mm was undersized for the load. but having done the calculations and thought about it I'm not quite sure any thoughts.
7.3kw + 2.3kw = Toal Max Load of 9.6KW = 41.7amps
Diversity applied(no socket at cooker switch) 10A + 30% remainder 10+9.51 = 19.51
with diversity applied Ib <In<It
can't find any reference in the regs to a 4mm cooker radial protected via 32amp MCB as the standard is 6mm/32mcb. Not standard circuit arrangement but as 4mmT+E can carry 37 Amps (ref C) I'm thinking that the additional load may be added.
i advised that for the hob to be installed the cooker radial would have to be rewired using 6mm T+E as the 4mm was undersized for the load. but having done the calculations and thought about it I'm not quite sure any thoughts.
7.3kw + 2.3kw = Toal Max Load of 9.6KW = 41.7amps
Diversity applied(no socket at cooker switch) 10A + 30% remainder 10+9.51 = 19.51
with diversity applied Ib <In<It
can't find any reference in the regs to a 4mm cooker radial protected via 32amp MCB as the standard is 6mm/32mcb. Not standard circuit arrangement but as 4mmT+E can carry 37 Amps (ref C) I'm thinking that the additional load may be added.