21 ohms is useless if you're relying on it to make fault disconnection times with no other parallel paths. We just installed a local earth at a remote pumping station, took 64 x 2.4m rods in 4 separate earth pits and 70m of 25mm earth wire to achieve a sub-ohm Ra. As Davesparks says a single rod won't help.
 
Zs = 21 ohms at a socket on db.( my mistake before calling it ze) 3 phase tt supply. No earth rod. Supply goes from rcd main switch to metal clase switched fuse. Swa then across yard to db in a shed. Did notice where db was that the steel work of building was bonded, so i think this would be giving a low reading. So if i put rod at mains and get a low reading do i need to put one at every board even if i get a low reading. Thanks

Basically you have an incoming DNO supply without any earthing, so if you have no earth electrode connection of any description at the source then it isn't even a TT system.... Seems the whole electrical system is relying on bonding connections, probably the water supply for the farmhouse and steelwork for this steel framed horse barn. I can see this situation turning into quite an expensive operation to rectify, and one that the farmer ain't gonna be too happy about, seeing how they hate spending money for something/anything they can't actually see.

Where livestock is concerned, things need to be done correctly, our 4 legged friends don't normally get to have second chances!!
 
21 ohms is useless if you're relying on it to make fault disconnection times with no other parallel paths. We just installed a local earth at a remote pumping station, took 64 x 2.4m rods in 4 separate earth pits and 70m of 25mm earth wire to achieve a sub-ohm Ra. As Davesparks says a single rod won't help.

I think you've frightened the crap out of him!! lol!!

Perhaps you should have mentioned that you are driving rods into compacted sand, and needed to go that deep (38+m) X 4...
 
I think you've frightened the crap out of him!! lol!!

Perhaps you should have mentioned that you are driving rods into compacted sand, and needed to go that deep (38+m) X 4...
[ElectriciansForums.net] tt earthing on farm
We had 4 rods per pit, each one was 4 rods coupled together and we angled the rods at about 20degrees from vertical so the depth of each rod was only around 8 meters. I wish it was sand but alas it was half way up a mountain so very rocky. Even digging the pit was a job for jackhammers and pickaxes. We deliberately used the thinner 5/8" rods because they deviate more readily when they hit rock, the other option is a 1 1/2" rod which will go through rock but there was no way to get a pneumatic driver up there.


Final Ra was 0.092ohms (worst result of 3 tests) after soaking the pits to backfill them. I've got to go back and confirmation test in 3 months and again in a year. Should breeze the 3 month test because it will be mid-winter and very wet, the 1 year retest should be the interesting one.
 
View attachment 28457
We had 4 rods per pit, each one was 4 rods coupled together and we angled the rods at about 20degrees from vertical so the depth of each rod was only around 8 meters. I wish it was sand but alas it was half way up a mountain so very rocky. Even digging the pit was a job for jackhammers and pickaxes. We deliberately used the thinner 5/8" rods because they deviate more readily when they hit rock, the other option is a 1 1/2" rod which will go through rock but there was no way to get a pneumatic driver up there.


Final Ra was 0.092ohms (worst result of 3 tests) after soaking the pits to backfill them. I've got to go back and confirmation test in 3 months and again in a year. Should breeze the 3 month test because it will be mid-winter and very wet, the 1 year retest should be the interesting one.

Hang on, you said you used 64 rods in 4 pit locations, that to my calculation is 16 rods a per pit??

''took 64 x 2.4m rods in 4 separate earth pits''

 
I’ve got this silly image in my mind of Marvo belting rods in and hitting rock that bend the rods back upwards, they appear out of the ground behind him.

Sorry kid.
 
It wouldn't be the first time, we knocked a rod in once at the corner of a factory unit and it surfaced about 12m away in the middle of the car park. You never really know how deep or what direction they go unless it's sand or unless you use large diameter rods like 1 1/2" or 2", with the 5/8ths rods it's just a numbers game where some will go straightish and some will deviate toward horizontal.
 
Something I wished I’d tried at the foundry.

Push a 6” nail in and see what reading it would give. The ground was full of iron oxide, carbon, sulphur, lime slag and to make it fun, cyanide.


PS, the land is up for sale as a prime building site, don’t take up gardening.
 

Reply to tt earthing on farm in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
753

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
703
You would treat it as a TT installation.
2
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top