Using IEC reference method A and B for loose wires in conduit a I have derived the following max OCPD and in turn maximum current loading for general use circuits:

1.5mm2: 10 amp MCB reference method A, 16 amp MCB reference method B

2.5mm2: 20 amp MCB (Both A & B)

4mm2: 25 amp MCB reference method A; 32 amp MCB Reference B

6mm2: 32 amp MCB reference method A, 40 amp MCB reference method B

10mm2: 40 amp MCB reference method A, 50 amp MCB reference method B

16mm2: 63 amp MCB reference method A, 70 amp MCB reference method B


Do my numbers sound correct? I may have rounded a few numbers in method B, so A would probably be the best approach. Just double checking.
 
Last edited by a moderator:
Does this mean the OCPD determines the current or the load? I may need an example.

You work out the design current, which is the current required by the load.
Then you select an OCPD which is equal to or higher than this current, this is the nominal current.
You then apply the cable rating factors to the nominal current which gives you the minimum permissible tabulated current carrying capacity of the cable.
You then select a cable size from the appropriate table which has a current carrying capacity equal to or greater than the required minimum.
You then use the tabulated voltage drop to confirm whether this will comply.
 
You work out the design current, which is the current required by the load.
Then you select an OCPD which is equal to or higher than this current, this is the nominal current.
You then apply the cable rating factors to the nominal current which gives you the minimum permissible tabulated current carrying capacity of the cable.
You then select a cable size from the appropriate table which has a current carrying capacity equal to or greater than the required minimum.
You then use the tabulated voltage drop to confirm whether this will comply.

Ok so:

A 5kw imersion heater, 5000/230=22amps. This would equate to a 25 amp MCB being the next standard size up. Thus my nominal current is not the load current but rather my MCB rating, so I would examine my installation method and base that off of 25 amps. Assuming 3 wires (L+N+E) in conduit in a thermall insualted wall with the conduit touching the inner surface I would use IEC refernce A giving me 4mm2 copper wire.

Assuming for example a 15 meter run and using V= {2I (Rc cos + Xc sin) L}/1000 I get a voltage drop of about 4 volts of 1.6%, which as long as it does not exceed 5% this is ok?

Sound about right?

And my earth fault loop impedance calculation assumes a conductor temprature of 70*Celcuis?
 
Load, breaker wire? Im confused lol.
[ElectriciansForums.net] Reference method A & B current rating


[ElectriciansForums.net] Reference method A & B current rating
 
Last edited:
Ok so:

A 5kw imersion heater, 5000/230=22amps. This would equate to a 25 amp MCB being the next standard size up. Thus my nominal current is not the load current but rather my MCB rating, so I would examine my installation method and base that off of 25 amps. Assuming 3 wires (L+N+E) in conduit in a thermall insualted wall with the conduit touching the inner surface I would use IEC refernce A giving me 4mm2 copper wire.

Assuming for example a 15 meter run and using V= {2I (Rc cos + Xc sin) L}/1000 I get a voltage drop of about 4 volts of 1.6%, which as long as it does not exceed 5% this is ok?

Sound about right?

And my earth fault loop impedance calculation assumes a conductor temprature of 70*Celcuis?
Sounds generally good to me, some minor notes (which don't affect the overall outcome):

(1) 25A MCBs are not common, you might struggle to find one, generally your choice is 20A or 32A

(2) The design is for a fixed load, and so overload protection is not required. The load on the circuit will not increase unless the heater is replaced by one having a higher rating, in which case you'll need to check the adequacy of the circuit. The OCPD in this case is for protection against fault currents only. Hence it is your design current, Ib (=22A), not the rated current of the protective device, In (=25A, or more realistically, 32A) that you use, so:

It >= Ib/(Ca Cg Cs Cd Ci Cc)

You would still end up with the same CSA (=4mm2)

(3) In determining voltage drop, it is always the design current (rather than the rated current of the protective device) that you use. From table 4D1A of BS 7671, VD = 11mV/A/m (ref A&B, 2 cable, single phase ac) = 11 x 22 x 15 = 3.63V, which as you say is fine.

(4) You mention "3 wires (L + N + E)", for the sake of clarity, the "E" wire is not "counted" when looking up the number of wires in the table. The current-carrying cables, the live ones, are the ones that count.
 
Ok thanks! :D

Over load proection is not required for all fixed in place applainces some are exampt? So In theory it is ok to have a higher MCB relative to the current carrying capacity of the wire provided the load does not exceed the capcity of the wire and the breaker is only upsized because the next required size not avaliable? However anything to a socket must have over load protection so the current carry capcity must be equal to or greater than the MCB?

Good point on not counting the E. It never should be. My understaning, and correct me if I am wrong, is that in a 3P+N circuit the neutral is not counted as a current carry conductor for de-rating unless the load in none linear in wave form?
 
Last edited by a moderator:
Regarding your first paragraph, basically, yes... although it's not that some are "exempt", it's just that if it's a fixed load, you know what the load is. If there are socket-outlets, then you don't know what the load is (depends on what's plugged in).

[ElectriciansForums.net] Reference method A & B current rating

Regarding your second point, you've got that spot on. Third order harmonics (and higher), even in a balanced 3P system, mean you'll get a neutral current and this needs to be taken into account in the rating factor.
 

Reply to Reference method A & B current rating in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top