Afternoon all..

I have just completed an EICR and came across the following :

[ElectriciansForums.net] TN-S with a BS951 clamp and black tar covering supply cable?[ElectriciansForums.net] TN-S with a BS951 clamp and black tar covering supply cable?

1. Is the black tarry substance Pitch?
The homeowner is unsure how long it has been there, however it is not completely solid and is slightly sticky to touch indicating that it is still getting too hot at times and leaking? I will be contacting DNO but wanted to get some more information from those who are experienced with this?

Max demand is approx 50A so I would be more concerned with loose connections in the DNO's equipment.

2. TN-S is supplied by a BS951 clamp which I understand was done for a period. My concern is that the 6mm bare cable from the clamp to the MET is just connected to the sleeve of the clamp that is moveable. It is a firm connection to that part of the clamp via the bolt, but just looks awful. I'll tell the DNO about this as well but again wanted some opinions please?

Ze = 0.17Ω
Cut out fuse 100A (not actually seen - but stated on cut out)

Thanks.
 
Wow.. Southern Electric move fast!

Just got off the phone to them and they are going straight around..

They will always attend site if it's leaking pitch. whilst southern electric are there get them to install the correct earth clamp for the incoming cable for the main earth connection.
 
Last edited:
Just contacted Southern electric for an update.. actually on the phone at the mo!

They say nothing wrong?

Is leaking Pitch ok?

Is that connection to the clamp ok?
 
No.
It would normally suggest overheating within the Cutout joint
Are there any Children in the household, or any that visit..

Well they have said because it is not dripping or hot that it is not an emergency which I guess makes sense. My concern is that they are planning on leaving it like that without doing anything else. Unfortunately my inexperience lets me down here and I dont know if I'm making a mountain out of a mole hill!

I have been given another number to ring on monday and they state they may then send someone out to do some work if needed, but they have basically said all is fine and will only make another visit if I ring and ask.

Also, I cant believe that clamp connection is ok. I can understand that BS951 clamps were used for a while, but that is not my worry. It is the way it is connected to the clamp. Again.. not an emergency as Ze=0.14, but it's hardly a very stable looking connection to the flapping sleeve of the clamp is it??

As for children.... Yes.... 2, one aged 6 and another aged 10!
 
Last edited:
That doesn't look like a bs951 clamp, it looks more like one of the older mechanical clamps for lead cable. Have a proper look at the construction of it to be sure. The construction of the lead clamps is a bit different to a 951 clamp with a curved plate to fit snug against the lead and not crush it. Clamps like that are not uncommon in the SSE area.
Also that is not a 6mm bare conductor, it's an imperial, probably 7/029, conductor.
 
That doesn't look like a bs951 clamp, it looks more like one of the older mechanical clamps for lead cable. Have a proper look at the construction of it to be sure. The construction of the lead clamps is a bit different to a 951 clamp with a curved plate to fit snug against the lead and not crush it. Clamps like that are not uncommon in the SSE area.
Also that is not a 6mm bare conductor, it's an imperial, probably 7/029, conductor.

Thanks Dave,

It does look slightly different to a 951. It is more they way it is connected. Can you see from the picture what I am getting at? The fact that it is connected to the flapping sleeve rather than firmly against the clamp as you would see with a 951?

[ElectriciansForums.net] TN-S with a BS951 clamp and black tar covering supply cable?
 
If there's no overheating detectable it will probably last years or even decades as it is so I wouldn't lose sleep over it. I'd still call them or get the customer to call them on Monday and insist they make the repairs and upgrade the earth connection.
 
That doesn't look like a bs951 clamp, it looks more like one of the older mechanical clamps for lead cable. Have a proper look at the construction of it to be sure. The construction of the lead clamps is a bit different to a 951 clamp with a curved plate to fit snug against the lead and not crush it. Clamps like that are not uncommon in the SSE area.
Also that is not a 6mm bare conductor, it's an imperial, probably 7/029, conductor.

Why 7/029? It looks bigger than that I think. That equates to 2.98mm and it looks bigger, possibly 7/036?

Adiabatic shows that CPC needs to be 3.63mm or above!

I have a fancy pair of calipers that usually show me the CSA if in doubt, but with 7 old tangled strands it's difficult!
 
If there's no overheating detectable it will probably last years or even decades as it is so I wouldn't lose sleep over it. I'd still call them or get the customer to call them on Monday and insist they make the repairs and upgrade the earth connection.

Thanks for that Marvo.

I will call them on monday and push it a little I think. I think it would be wrong to just think 'oh well, I've called the DNO it's their responsibilty now'.
 
Why 7/029? It looks bigger than that I think. That equates to 2.98mm and it looks bigger, possibly 7/036?

Adiabatic shows that CPC needs to be 3.63mm or above!

I have a fancy pair of calipers that usually show me the CSA if in doubt, but with 7 old tangled strands it's difficult!
But what is the copper equivalent csa of a 10mm x 0.5mm strip of flexible steel?
 

Reply to TN-S with a BS951 clamp and black tar covering supply cable? in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
TN-S with a BS951 clamp and black tar covering supply cable?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
29
Unsolved
--
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top