Afternoon all..

I have just completed an EICR and came across the following :

[ElectriciansForums.net] TN-S with a BS951 clamp and black tar covering supply cable?[ElectriciansForums.net] TN-S with a BS951 clamp and black tar covering supply cable?

1. Is the black tarry substance Pitch?
The homeowner is unsure how long it has been there, however it is not completely solid and is slightly sticky to touch indicating that it is still getting too hot at times and leaking? I will be contacting DNO but wanted to get some more information from those who are experienced with this?

Max demand is approx 50A so I would be more concerned with loose connections in the DNO's equipment.

2. TN-S is supplied by a BS951 clamp which I understand was done for a period. My concern is that the 6mm bare cable from the clamp to the MET is just connected to the sleeve of the clamp that is moveable. It is a firm connection to that part of the clamp via the bolt, but just looks awful. I'll tell the DNO about this as well but again wanted some opinions please?

Ze = 0.17Ω
Cut out fuse 100A (not actually seen - but stated on cut out)

Thanks.
 
Why 7/029? It looks bigger than that I think. That equates to 2.98mm and it looks bigger, possibly 7/036?

Adiabatic shows that CPC needs to be 3.63mm or above!

I have a fancy pair of calipers that usually show me the CSA if in doubt, but with 7 old tangled strands it's difficult!

You might be right, I've got the old regulations at home so I can look up what the required size was at the time, it may be 7/044.
 
Thanks Dave,

It does look slightly different to a 951. It is more they way it is connected. Can you see from the picture what I am getting at? The fact that it is connected to the flapping sleeve rather than firmly against the clamp as you would see with a 951?

I am familiar with that type of clamp yes, it's quite common in the SSE area. There is another one which is just that length of that band wrapped round the lead sheath with a bolt and two wedge shaped nuts to hold it tight, then a nut and bolt with a castle washer through the band in exactly the same way.
Is there a castle washer on that termination?
 
But what is the copper equivalent csa of a 10mm x 0.5mm strip of flexible steel?

Oh Richard!!!!

Well if copper is rated at 100% (because Copper is the standard by which electrical materials are rated), and we take steel as 15 (I'm being optomistic as it 3-15%) then steel is only 3/20 as conductive as copper.

If the clamp is 10mm x 0.5 it has a csa of 5mm.

5mm x (3/20) = 0.7mm (equivalent of copper)..

In otherwords 'way too small'!!

Of course thats all far too simplistic and ignoring many other factors that I dont understand.. A clamp MUST be a better conductor than 3/20 of copper otherwise we wouldn't use them as a bonding clamp!
 
Oh Richard!!!!

Well if copper is rated at 100% (because Copper is the standard by which electrical materials are rated), and we take steel as 15 (I'm being optomistic as it 3-15%) then steel is only 3/20 as conductive as copper.

If the clamp is 10mm x 0.5 it has a csa of 5mm.

5mm x (3/20) = 0.7mm (equivalent of copper)..

In otherwords 'way too small'!!

Of course thats all far too simplistic and ignoring many other factors that I dont understand.. A clamp MUST be a better conductor than 3/20 of copper otherwise we wouldn't use them as a bonding clamp!

... well, a clamp is a ring ... therefore ... still way too small!
 
Last edited:
I am familiar with that type of clamp yes, it's quite common in the SSE area. There is another one which is just that length of that band wrapped round the lead sheath with a bolt and two wedge shaped nuts to hold it tight, then a nut and bolt with a castle washer through the band in exactly the same way.
Is there a castle washer on that termination?

I'm sorry Dave, I dont know.
 
... well, a clamp is a ring ... therefore ... still way too small!

Not the clamp itself, the sleeve.. which is 10mmx0.5mm (approx)(so CSA of 5mm².. this is what the fault current will pass through. If the CPC was attached to the clamp in the usual way as it is with a BS951 then I wouldn't be as worried as there would be a much larger CSA for fault current to pass through as the current would utilise more of the clamp.
 
Last edited:
Oh Richard!!!!

Well if copper is rated at 100% (because Copper is the standard by which electrical materials are rated), and we take steel as 15 (I'm being optomistic as it 3-15%) then steel is only 3/20 as conductive as copper.

If the clamp is 10mm x 0.5 it has a csa of 5mm.

5mm x (3/20) = 0.7mm (equivalent of copper)..

In otherwords 'way too small'!!

Of course thats all far too simplistic and ignoring many other factors that I dont understand.. A clamp MUST be a better conductor than 3/20 of copper otherwise we wouldn't use them as a bonding clamp!
k1/k2 * S
k1 for copper is 143, k2 for steel is 51, S= 3.63mm²
so S for steel needs to be (143/51)*3.63 = 10mm², you only have 5mm² (approx)

Hope they actually do something about it.
 
Thanks Richard..

Of course!! I'd only just been looking at table 54.2!

I've never used the K factor for steel before.. and there was me trying to be all clever with conductivity ratios.. just looking foolish really! :smile5:
 
Last edited:
Not the clamp itself, the sleeve.. which is 10mmx0.5mm (approx)(so CSA of 5mm².. this is what the fault current will pass through. If the CPC was attached to the clamp in the usual way as it is with a BS951 then I wouldn't be as worried as there would be a much larger CSA for fault current to pass through as the current would utilise more of the clamp.

There shouldn't be a cpc connected to the clamp at all!
 

Reply to TN-S with a BS951 clamp and black tar covering supply cable? in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
TN-S with a BS951 clamp and black tar covering supply cable?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
29
Unsolved
--
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top