As I promised I would try and post things on here in the hope it might help some of the lads that perhaps don't do larger jobs

Below is another of my builds here. This one is different from the first in that it is a metal framed prefab made of external sandwich panels The left is the steel work going up, the right is this morning 2 weeks later!


[ElectriciansForums.net] 2 Weeks here...........[ElectriciansForums.net] 2 Weeks here...........

Because it is steel framed I have slighlty different earthing issues as I need to bond the frame. The left hand picture is the Bond for the building.
I sized originally a 50mm but we literally had 70mm on the "van" so I used that. The middle picture is entry back into the building from my earth pits, Eventually it will be a manhole and the lightning/functional earth/bonding will all come back into the building and then onto the MET.
The right hand picture is one side of the building that is being compacted and where I will put 3 pits and rods.


[ElectriciansForums.net] 2 Weeks here...........[ElectriciansForums.net] 2 Weeks here...........[ElectriciansForums.net] 2 Weeks here...........

These final 2 pictures are going to be too large ops rooms. Originally I designed a floating floor and using power trunking, because I wanted the flexibility of moving desks etc around. Unfortunately out here there is a 16-18 week lead time for power trunking, and the occupancy is scheduled for January. So we have had to go back to floor boxes for power/data and we are using DADO trunking for the wall mounts

[ElectriciansForums.net] 2 Weeks here...........[ElectriciansForums.net] 2 Weeks here...........

I'll try and take more pictures as the build progresses
 
As promised will try and post various stages of the install.

We have now started to do the hangers for the containment. Picture on the right is looking down the corridor. The length is 42 metres. The left one shows the entrance of the building, the technical room will be at the back. So the left is the end of the run with a lonely 4 x 4 piece of trunking there. We are going to run the first 20mts in 6 x 6 and the last 22 in 4 x 4


[ElectriciansForums.net] 2 Weeks here...........[ElectriciansForums.net] 2 Weeks here...........

The one below is the pull boxes that will connect with the trunking. Again we will use ally flexible conduit to join with the trunking.

The 2 conduits marked with masking tape are power conduits. That tape is denoting the panel and circuit. So it is MDPL/R2-6, we still use red yellow blue here. These bits of tape will be removed and a proper label will be fitted just because for no other reason as that is what I want lol

[ElectriciansForums.net] 2 Weeks here...........

I've added the bottom one simply because I wanted to show one way of omitting RCD protection. The drop is a light switch and controller for dimmable HF flourescent 60 x 60 modules. I was a little concerned with using RCBO protection on these, so achieved the non rcd rule by burying the conduits below 50mm

[ElectriciansForums.net] 2 Weeks here...........

PS......................don't look at the site lighting...................you sometimes just have to let things ride over here
 
Last edited:
Carry on with this building

[ElectriciansForums.net] 2 Weeks here...........[ElectriciansForums.net] 2 Weeks here...........[ElectriciansForums.net] 2 Weeks here...........

We are now virtually finished inside just a few odds and sods. We have run the DATA and power in DADO, which is quite a new thing for my lads, so they had made quite a decent fist of it, after a couple of attempts.

[ElectriciansForums.net] 2 Weeks here...........

Here is the joining section to capture the tray, again I think they did a decent job

And all we have to do now then is sort this lot out, once the external plant room is built

[ElectriciansForums.net] 2 Weeks here...........
 
its a good idea to stop the tray short, that will be a ****** to pull off now.


in all the hospital jobs ive seen then float copex off the basket/tray/trunking into the dado.
 
Last edited by a moderator:

Reply to 2 Weeks here........... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
No mate, it was more out of curiosity than anything else. I see plenty in the high rise blocks that we fibre up that makes me cringe. See plenty...
Replies
3
Views
464
  • Question
I recently had similar but my 2 supplies were from different transformers going into different ends of a long property divided in two. Western...
Replies
11
Views
2K
  • Question
I would have to agree with @James to hire an electrician to measure the voltage coming in to the panel. If you have 240vac phase to phase then you...
Replies
3
Views
842
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
825
  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks