Had to rewire some outside lights in a house. Was told that recently installed car charging point keeps tripping out an MCB. Find this absolute monstrosity.
This photo shows a garage board which is fed off the main fuse board on a 6mm twin 50A mcb. Yay. If you look at the main switch, you'll see a 16mm core on the supply side, which the car charging point firm tapped off and sent the feed to the smaller enclosure which is to the left of the picture.
Out of shot, there is a 8 way garden lighting DB, which is fed from this garage board on the 32A breaker.
Basically, all of this is powered by a 6mm cable. Which the most recent addition was a 40A supply for a car charging point. Installed when surely they knew the circuit was at its limit.
I am recently qualified and unearthed all of this. Any suggestions? Thinking a 16mm SWA from mains supply isolated, to feed these two boards?