Had to rewire some outside lights in a house. Was told that recently installed car charging point keeps tripping out an MCB. Find this absolute monstrosity.

This photo shows a garage board which is fed off the main fuse board on a 6mm twin 50A mcb. Yay. If you look at the main switch, you'll see a 16mm core on the supply side, which the car charging point firm tapped off and sent the feed to the smaller enclosure which is to the left of the picture.

Out of shot, there is a 8 way garden lighting DB, which is fed from this garage board on the 32A breaker.

Basically, all of this is powered by a 6mm cable. Which the most recent addition was a 40A supply for a car charging point. Installed when surely they knew the circuit was at its limit.

I am recently qualified and unearthed all of this. Any suggestions? Thinking a 16mm SWA from mains supply isolated, to feed these two boards?
 

Attachments

  • [ElectriciansForums.net] Yeeehaaaw
    1470387154047471339246.jpg
    325.3 KB · Views: 253
It is rough a bit.
Do they use the charger ,or more likely ,was it a freebie?

I have seen one installed with SY , no glands on braid , and cut through straight into the side of CU . No support to charger . Lovely job.
 
If they will not allow you the time to do anything with it then there is nothing you can do.

Tel has outlined the ideal solution, but I have the feeling it is out of your hands.
I would like to bet that this has been sprung on you at the last minute , and it has been tripping for ages . It is a typical knee jerk.
 
tell him that that DB does not comply , it needs ripping out before you'll put your name to the job. compare working with that to building a house on cinder block foundations instead of concrete.
 
you can polish a turd, but you can't make a banana from a turd, polished or not. @OP. do it right or walk away and let some silly arse cowboy take the fall
 
I'm a bit confused.

...This photo shows a garage board which is fed off the main fuse board on a 6mm twin 50A mcb.

Sorry, I can't see a 50A MCB. Which one is it?


...Which the most recent addition was a 40A supply for a car charging point.

Again, is there a 40A MCB, or is the charging point on the 32A?
 
Last edited:

Reply to Yeeehaaaw in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
364
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
330
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
371

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
667
Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
288

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top