Discuss EICR meter tails coding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
6mm single core cables can take 47A clipped direct, Mr Nicholas, so with a 60A main fuse I'd be inclined to say a C2 because it could be dangerous with a large load. However, I'm still learning in this game so I'd see what others say too.
Also, pretty sure there's some argument out there that tails can have a CCC less than the main fuse provided the maximum demand of the property isn't going to pull more than the tails can handle.
Just to throw a spanner in the works but the meter tails are technically owned by the supplier so a c2'isn't really appears as you can't fix them.
Just to throw a spanner in the works but the meter tails are technically owned by the supplier so a c2'isn't really appears as you can't fix them.
A note on the cert imho
Meter tails yes, but OP means consumer unit tails which are the belonging of the consumer.
The meter to CCU maybe the consumers but you can't change them without breaking the meter seals
Tails out going are supplied by the contractor. But they are connected.!Look at least 10mm maybe 16mm my eyes aint good.Just to throw a spanner in the works but the meter tails are technically owned by the supplier so a c2'isn't really appears as you can't fix them.
A note on the cert imho