Hi all some advice please been asked to carry out A eicr on a flat the flat is in a care home 27 flats seems like when it was bulit non of them have had a earth run to them jusy l n tails only and the earth is taken from the neutral via a Henley block am I right in saying it's a c2? Going by reg 543.1 It's a pme system
 
Then a PEN conductor is not permitted apart from a DNO supply cable.
Without looking they maybe other exceptions however the set up you are testing it would not be permitted.
How old is the installation?
 
Thanks Ian I gave it a c2 for the reasons u said just wanted to hear others views say good 30 years old install the client is worried as each flat has same issue
 
As far as I'm aware a PEN conductor is permitted on a private supply transformer only which would be the DNOs.
I find the set up you've described quite worrying really if all the flats are like this?
Is there a main earthing conductor at the supply intake were the supply comes in and connects to the metering equipment?
 
Yer there is also main gas and water to bulidmg is bonded to the main met just each flat has no earth got me thinking how did they pass it at the time seem to come across a few in the east London areas
 
Whilst you cannot install a PEN conductor these days, it is permissible to maintain an existing installation and the requirements for such are still in bs7671 as far as I know.
So you can't, to the best of my knowledge, give it a code based purely on it being this type of installation.
 
The problem I got is I need to change the ccu within the flat as well as carrying out a eicr guess I got no choice but to run a 16mm earth in
 
I disagree.
A lost neutral to the flat would result in possible full mains voltage appearing across the cpcs connected directly to the neutral inside the flat.
I believe it to be a potentially dangerous situation the way it is now.
 

Reply to Eicr advise needed please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top