because we should aim for fault protection to be provided by the OCPD, not reliant on a RCD.If the maximum zs is okay up until 1667 ohms protected by a rcd why do we care about maximum disconnection times for the mcbs e.g why do we test and it's important to meet 1.37 or 1.1 zs on a 32 amp circuit
If the maximum zs is okay up until 1667 ohms protected by a rcd why do we care about maximum disconnection times for the mcbs e.g why do we test and it's important to meet 1.37 or 1.1 zs on a 32 amp circuit
Well if it's a TN type earthing system , you got to wonder why the zs readings are high?If it's a split load board is there any reason to worry if the zs readings are higher then the mcbs specified
not the point. using the RCD as fault protection is at best a fudge, and at worst, dangerous. a circuit that should give a Zs reading of, say, sub 1.0 ohms and has a reading of 4.0 ohms may have a bad connection that could lead to arcing and a possible fire risk.Well if it's a TN type earthing system , you got to wonder why the zs readings are high?
You will of course be covered by a dual rcd consumer unit providing the necessary fault protection for your 0.4 or 5 second disconnection times
Not disputing that , just that there will be fault protection afforded by the rcd, I did say you've got to wonder why you have a high zs reading on especially a TN systemnot the point. using the RCD as fault protection is at best a fudge, and at worst, dangerous. a circuit that should give a Zs reading of, say, sub 1.0 ohms and has a reading of 4.0 ohms may have a bad connection that could lead to arcing and a possible fire risk.
No this is just me wondering.im doing a eicr around the house and worrying about high zs readings looking for loose connections and I'm wondering why is the regulations even there to abide by.i can't think why it matters if the readings are over the maximum zs readings as theirs a rcd split load preotecting them .