I want same electrical work done, it's not new works just replacement as in I don't want single light pendants in my hallways I want downlighters,a couple surface mounted cables buried and surface mounted sockets moved down and sunk in the wall. The fella is telling me that I need a new whole new fuse box because that's the new regs. I didn't think downlighters had to be RCD protected. This is a picture of my box and I believe that it doesn't need replacing.

[ElectriciansForums.net] Is this a bit of a stitch-up
 
If he is going to intern cables in the wall without earth containment then yes they require additional rcd protection. How he goes about this is either a board update or provide rcd protection by other means. It should be noted that right side mcb does not belong in that board.
 
I forgot to mention that after I said I'm suppling the lights sockets and switches he said he'd knock ÂŁ200 off. Now what I bought came to ÂŁ57 and that's at retail.
What with his trade discount he does have quite a mark up. I don't begrudge anyone making a living but surely he's wants enough at ÂŁ50 a hole for the 8 downlighters. I don't think my pasterboard ceiling is reinforced with concrete. And upto ÂŁ125 for chasing, after telling me that his great chasing machine will do it in a few minutes and with no mess.
 
I forgot to mention that after I said I'm suppling the lights sockets and switches he said he'd knock ÂŁ200 off. Now what I bought came to ÂŁ57 and that's at retail. What with his trade discount he does have quite a mark up. I don't begrudge anyone making a living but surely he's wants enough at ÂŁ50 a hole for the 8 downlighters. I don't think my pasterboard ceiling is reinforced with concrete. And upto ÂŁ125 for chasing, after telling me that his great chasing machine will do it in a few minutes and with no mess.

Get another quote, we can't judge from here how much work is involved.

Edit, also if I were doing the work and you supplied me what I presume are cheap nasty, awful to fit down lights you'd purchased yourself, I'd charge more. I'd also not offer any warranty on them.
 

Reply to Is this a bit of a stitch-up in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

  • Question
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
Replies
8
Views
1K
It won't be notifiable though as its not a new circuit, if you change the the tails from 16mm to 25mm is that notifiable? No, if you add an...
Replies
5
Views
432

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top