Cooker supply 12kw correct cable size | Page 3 | on ElectriciansForums

Discuss Cooker supply 12kw correct cable size in the UK Electrical Forum area at ElectriciansForums.net

Adamk

-
Joined
Dec 17, 2017
Messages
9
Reaction score
3
Location
London
Hey guys

I’ve run a 6mm for a cooker, runs about 10metres. The customers has changed her mind on the cooker and gone for a 12kw range. Went back today to finish off and saw this lovely surprise. I know you have to take diversity into account. But for my peace of mind. Would 6mm 32a MCB be fine?

Kind of panicking a bit as the jobs finished.

What you think? Please dont tell me to tell her to change it as that’s not really an option :( Thanks
 
I've been meaning to clamp the thing on start up, just to see how many amps its pulling and for how long.

Well really bored and run out of [ElectriciansForums.net] Cooker supply 12kw correct cable size So decided to clamp our 8.6kW cooker. Now meter's bit of a cheapie, and probably needs calibrating. But here's what I got on 244V; 39.4A.

By my calcu's should of been tad over 35A. Run it for a min or so, to allow things to settle.
 
Well really bored and run out of View attachment 39827 So decided to clamp our 8.6kW cooker. Now meter's bit of a cheapie, and probably needs calibrating. But here's what I got on 244V; 39.4A.

By my calcu's should of been tad over 35A. Run it for a min or so, to allow things to settle.

It takes more than a minute for the thermostats to start cutting out and back in which gives the diversity in the cooker.

Diversity takes in to account the fact that when cooking you don’t turn everything on at once, different things take different times to cook so in real use not all elements are switched on at once.
 
Hasn’t took diversity into account... he’s just done 8600/240 which isn’t correct.... but mainly causes he’s ran out of beer

But he's just done what he suggested... "'I've been meaning to clamp the thing on start up, just to see how many amps its pulling and for how long"...
 
Okay so I couldn't be arse'd to stand out in the cold for your aresholes to allow the thermostats to cut in etc. Point I was trying to make was worst case situation, was max amps. Still be happy to connect to 32A 6mm supply. Jesus opps Holy Mary, cripes just be a bit more little horizontal you lot, its Xmas :rolleyes:
 
Okay so I couldn't be arse'd to stand out in the cold for your aresholes to allow the thermostats to cut in etc. Point I was trying to make was worst case situation, was max amps. Still be happy to connect to 32A 6mm supply. Jesus opps Holy Mary, cripes just be a bit more little horizontal you lot, its Xmas :rolleyes:
you might notice that i made no comment on your previous post so far.
39A...........

[ElectriciansForums.net] Cooker supply 12kw correct cable size
 
Okay so I couldn't be arse'd to stand out in the cold for your aresholes to allow the thermostats to cut in etc. Point I was trying to make was worst case situation, was max amps. Still be happy to connect to 32A 6mm supply. Jesus opps Holy Mary, cripes just be a bit more little horizontal you lot, its Xmas :rolleyes:

I'm with you Middy. Except the running out of beer bit - do try harder!
 
I just fitted a rangemaster elan induction at home, instructions stipulated 10mm and 40A MCB, I wondered how id fair if I fitted it to a 6mm cable with warranty etc and at over 2 grand I wasn't taking chances. I commented to the missus that 6 of us grew up with four burners, 1 oven and an eye level grill that took your eyebrows every time you lit it with a match (or piece of paper!)
 
Now then Rangemaster. I had this one with a customer earlier this year.She had paid for delivery and fitment. On arrival fitter said its only 6mm cable needs to be 10mm and 40a breaker. It was returned and she contacted me. Silly thing was it was the new version of the one she was replacing.With divercity it was pushing 29.5 A. The Rangemaster book says 10mm and 40 a but if you dig on their web site it states they are ok on 6mm and 32A mcb. I presented her with a print off from the site. the next day the range and another sparky turned up, he agreed what she had been told was bull. He installed it tested it and went on his way. This pathetic Christmas dinner senario does not happen. This lady cookes a Massive meal every week end for 12+ people and has never tripped. I also did a clamp test on a new install and after 90 seconds with every thing switched on (4 induction rings and a fan oven/grill) the current dropped like a stone to single figures. You could if you wanted fit a 40A breaker to a 6mm cable under certain conditions is not a problem.
 

Reply to Cooker supply 12kw correct cable size in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top