Hey guys

I’ve run a 6mm for a cooker, runs about 10metres. The customers has changed her mind on the cooker and gone for a 12kw range. Went back today to finish off and saw this lovely surprise. I know you have to take diversity into account. But for my peace of mind. Would 6mm 32a MCB be fine?

Kind of panicking a bit as the jobs finished.

What you think? Please dont tell me to tell her to change it as that’s not really an option :( Thanks
 
I dunno, the guy who fitted mine was a gas safe fitter (mine has gas hobs). He did tell me off 'cos my old 2.2kW oven with manufactures 1.5mm flex was connected to my 40A 10mm supply via cooker connection unit. Should of been connected via 13amp FCU apparently :rolleyes:
 
I did have to refit an AGA all electric monster, about 18kW max load I think. It had been connected up by AGA persons in the old kitchen to a 32A 6mm supply, which had happily existed for a few months. When we refurbed, I ask by chance AGA technical what supply it should have, '45A 10mm'. So, I went down the middle, 32A ocpd & 10mm cable.
 
The 1.5mm via a CCU is much less preferable to a 13a FCU set up.
In reality The AGA 18kw monster would be fine on 6mm and a 32a breaker (under suitable conditions) as per BS7671 as diversity gives 30.5 amps. The diversity set up has been going for some 60 years and has stood the test of time.
 
Has anybody here ever fitted a domestic cooker on a 32A MCB and had problems with it tripping?

I must've fitted hundreds of cookers including some big lumps in the last 15 years and never had even one report of tripping through overload.
 

Reply to Cooker supply 12kw correct cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
4K
  • Question
Thanks both for your input. Sounds daft i know but we got the feeling on the phone that the manufacturer didn't have a clue either even though...
Replies
7
Views
6K
I’m not aware of any difference in diversity calcs based on circuit type. It’s done by appliance. Since a cooker circuit IS a radial anyways...
Replies
3
Views
4K
  • Question
It is probably OK as unlikely they would turn on everything at once. That 42A max on a 32A MCB would trip somewhere between around 1 and 10...
Replies
3
Views
1K
  • Question
This looks like a decent project to get your teeth into. It may be worth your while looking through the directory on here for your area as your...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks