I had a new kitchen fitted some months back and have never had any certificate for the job as promised. I am looking to get someone to test the house before selling up next year. Please can someone confirm if it appears ok what the chap did?
Kitchen wall was knocked down to create large kitchen dinner. Kitchen was a ring main with four sockets. Two sockets in the dining room were fed off a radial circuit from the front room. These were terminated and put on to the ring main. Diagram below:
The two fused spurs (dishwasher and extractor fan), each one is fed off one of the double gang sockets.
Junction box feeding outhouse - it has one double socket with a fused spur off it for a light.
Circuit is 2.5mm T+E on 32A MCB with RCD protection.