Part Rewire to do, small shop on a large premesis 4 lights, 2 sockets, 2 spurs...The existing DB(DB4) which is staying, is fed via 32A mcb from a sub main DB3. Fed by 63 A mcb in another DB2 which then goes to DB1 which is connected to origin. Took a while to chase through as all DBs are in seperate buildings. My question is how far would you go on the EIC in terms of inspect and test details of each protective devices and cable sizing in line etc as job will more difficult obviously access and isolating testibg at each point in 4 seprate buildings.
 
One schedule of inspections and test results stating which DB the DB you're working on is fed from with Zdb etc.
 
3 phs Cutout. All brown singles 35mm ish main earth looks 10mm appears to be undersized for installation. Ze 0 24
MainDB at cutout in main building feeds
DB1 seperate building 40 meters away
feeds
DB2 in an external outbuilding
Feeds
DB3 another outbuilding. Zdb 0.70 TNCS.
 
So DB4 which you are installing new circuits to is fed from DB3 via 32A MCB. What is the Zdb at this DB?as max Zs for a C 32 MCB is 0.68! and that's the 100% figure.
 
What type of Crabtree mcb is it. I agree discrimination is to pot but sometimes you can only work with what you have. If main protective bonding is required at your premises is the cpc of the supply cable to DB4 of a suitable csa to support bonding. I would check the supply cable from DB3 to 4 is adequately sized and whether fault protection is maintained by the supply protective device at DB3.
 
But i havnt checked cable sizes at each point in line to DB3. Again being in different buildings its alot of work to actually do, before doing the job you are being paid to do. Eg if the db1 or db2 had an underated cable or any other issues then connecting anything after these wouldnt be acceptable.
 

Reply to EIC for submain db rewire in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
753

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top