There is no other services ie water gas... in the building im part rewiring. They do however want another new DB to be fed from DB2 via another 32A mcb, to be located in a steel structure greenhouse for growing plants and veg so i assume may have sprinkler system. Anyone done anything in similar enviroment.
 
There is no other services ie water gas... in the building im part rewiring. They do however want another new DB to be fed from DB2 via another 32A mcb, to be located in a steel structure greenhouse for growing plants and veg so i assume may have sprinkler system. Anyone done anything in similar enviroment.
 
For your work you need to ensure the supply is suitable for the work you are doing and that the work you are doing is compliant, you also need to ensure that earthing and bonding is adequate for the protective measures you are using.
The 32A MCB you have stated at one point is supplying DB4 and you also seem to state it is supplying DB3.
If DB3 is supplied via a 32A type 2 MCB with Zdb of 0.70Ω and the cable incoming is suitable to carry 32A then this is compliant, except for the discrimination issues, which you cannot address.
You wish to add 4 sockets (circuits or individual sockets?), 2 spurs (presumably 13A?) and 4 lights (again circuits or individual lights).
If you are adding 4 individual sockets, 2 13A spurs and 4 individual lights then the supply could well be suitable for the load, depending on diversity since this is a shop it may have long term demand at full load.

The second DB to be installed in a greenhouse is more inconvenient, but you would need to ensure that the DB is protected against the external influences expected and bonding of the steel frame of the greenhouse may well be required, subject to appropriate assessment and testing. Therefore if that were the case then I would expect an additional bonding conductor would be needed.
 
My question wasnt about the correct way to install etc im aware of all points people have mentioned... More on how far would people go ensuring everything inline was adequate simply to provide just a quote and what tests would you carry out as could be very time consuming in this circumstance. Also on what details you would input on EIC as some have said they would only check submain woring on and mains. As we know alot would install without a thought. Explainig to clients isnt simple either, especially if it creates more work as "its been like that for years"will be their reaction...but taking into account all the points being made on adequacy of current installation etc would you just refuse to do anything unless all points are met. Thanks for replies peeps. In terms of discrimination it is as follows. I shouldve been more clear with details at start apologies...
Cutout
3phase 100A bs1361 feeds
DBmain (8 way)
3P MCB 60Amp 16mm4c (swa cpc) feeds
DB1 - 3Phase (8 way)
3P MCB 63A dont know cable size feeds
DB2 which has a 100A RCCB 30mA main switch and is 3 phase.
32 A single phase mcb (attached image) 6mm 3 c swa feeds
DB 3 which has 100A RCCB 30mA main switch single phase 5 way DB.. Think thats pretty accurate but is from memory as details are in the van which is outside and its cold .
 
My question wasnt about the correct way to install etc im aware of all points people have mentioned... More on how far would people go ensuring everything inline was adequate simply to provide just a quote and what tests would you carry out as could be very time consuming in this circumstance. Also on what details you would input on EIC as some have said they would only check submain woring on and mains. As we know alot would install without a thought. Explainig to clients isnt simple either, especially if it creates more work as "its been like that for years"will be their reaction...but taking into account all the points being made on adequacy of current installation etc would you just refuse to do anything unless all points are met. Thanks for replies peeps. In terms of discrimination it is as follows. I shouldve been more clear with details at start apologies...
Cutout
3phase 100A bs1361 feeds
DBmain (8 way)
3P MCB 60Amp 16mm4c (swa cpc) feeds
DB1 - 3Phase (8 way)
3P MCB 63A dont know cable size feeds
DB2 which has a 100A RCCB 30mA main switch and is 3 phase.
32 A single phase mcb (attached image) 6mm 3 c swa feeds
DB 3 which has 100A RCCB 30mA main switch single phase 5 way DB.. Think thats pretty accurate but is from memory as details are in the van which is outside and its cold .
That is very poor discrimination between RCD's if something with a earth fault is plugged in on DB3 this could trip out DB2.
 
So the situation changes again.
You have no discrimination between boards and you now have no discrimination between RCDs as well.
So a short circuit at DB3 could readily take out DB 2 as well.
An earth fault DB3 will also take out DB2.
However this is not what you are installing. Though you would need to check the RCD is working which will be a nightmare of overlap.
Since you are doing a rewire of a whole area, I would say that you should also attempt to find out the supply cable size between DB1 and DB2.
Then you will be able to enter the circuit description details of the submains on the EIC, Zdb only being relevant at DB3.
Full circuit details and tests would be needed for the circuits you are rewiring from DB3.
[ElectriciansForums.net] EIC for submain db rewire
 
That is very poor discrimination between RCD's if something with a earth fault is plugged in on DB3 this could trip out DB2.
Client says it occasionally trips at DB2 but it only feeds a couple of sockets and a light within the outbuilding the db is located in( which isnt occupied) and a greenhouse db so isnt a major inconvenience..
 
So the situation changes again.
You have no discrimination between boards and you now have no discrimination between RCDs as well.
So a short circuit at DB3 could readily take out DB 2 as well.
An earth fault DB3 will also take out DB2.
However this is not what you are installing. Though you would need to check the RCD is working which will be a nightmare of overlap.
Since you are doing a rewire of a whole area, I would say that you should also attempt to find out the supply cable size between DB1 and DB2.
Then you will be able to enter the circuit description details of the submains on the EIC, Zdb only being relevant at DB3.
Full circuit details and tests would be needed for the circuits you are rewiring from DB3.
View attachment 41417
Also the 63A @ db1 after the 60@ dbmain
 
Into DBmain from metering. Poor installation all round really. Main earth looks to be 10mm to met then 25mm into dbmain. Cant see incomer as 2 obsolete cables are cut sticking out covering it.

[ElectriciansForums.net] EIC for submain db rewire

[ElectriciansForums.net] EIC for submain db rewire
 
That looks a lot like one of the tails entering through a separate hole in the steel enclosure, so you’ve got another non-compliance.
That's it Dave kick him when he's down, these non-compliances are acuminating.And there is abrasive edge (no bush/Gromit to cable entry on left.
 
Observed, thats why i took the pic. Its Neutral and Earth. Also no lid for the trunking header which creates an Ip4x issue in top of db. I think these old brown tails are single insulated? Again where would you go with these. Observations on existing installation could be alot of work alone. These would hopefully have all been highlighted in the latest eicr.
 
Last edited:

Reply to EIC for submain db rewire in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
616
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
774
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top