So the situation changes again.
You have no discrimination between boards and you now have no discrimination between RCDs as well.
So a short circuit at DB3 could readily take out DB 2 as well.
An earth fault DB3 will also take out DB2.
However this is not what you are installing. Though you would need to check the RCD is working which will be a nightmare of overlap.
Since you are doing a rewire of a whole area, I would say that you should also attempt to find out the supply cable size between DB1 and DB2.
Then you will be able to enter the circuit description details of the submains on the EIC, Zdb only being relevant at DB3.
Full circuit details and tests would be needed for the circuits you are rewiring from DB3.
View attachment 41417