This has come up many times before and after a couple of hours reading previous posts I'm no closer to deciding on a code, note or nothing at all.

BS7671 allows 16mm tails on 100A fuse if demand is less than the cables CCC, I have 16mm at 94amps and the max demand is 60a.

From a previous post I've read UKPN state switched fuse OR ISOLATOR within 3mtrs.

Would you code, mention or no mention this?
 
You are assesong the job as per BS7671, nithing else so UKPN has no bearing on it. What you have to ask yourself is will the maximum demand ever chamge in the future seeing as the incoming fuses will allow it.
 
Thanks Guys,

I agree Dillb, and it is feasible as separate 6mm cable has been run for hob and oven, new home owners may decide to install induction hob and higher rating oven.

It is a gas hob atm and 13amp SFS for oven.
Oven at higher rating is probably unlikely as most modern ones are 16A max.

Either way it didn't sit right with me as I would have installed switched fuse at 80A. Still unsure on code though?
 
Im going to try to attach photos..
Other areas of concern are:

1) Un-enclosed SWA conductors - I guess it could be argued the meter cabinet is an enclosure opened by key. so maybe C3 not C2?

2) Main earth uses gas supply = C2
From suppliers terminal they have 10mm to first earth terminal, the 2x 10mm goes to water bond, the 2x 2.5mm go to SWA amour. Nothing connects to the other earth terminal! Which holds the 2x 16mm from the SWA and 2x 10mm Gas bonds. Therefore other than the gas the earth path is the 2x2.5mm to the amour.
 
[ElectriciansForums.net] 16mm SWA tails maybe 9 mtrs from isolator on a 100a supply, and other concerns - EICR opinions
[ElectriciansForums.net] 16mm SWA tails maybe 9 mtrs from isolator on a 100a supply, and other concerns - EICR opinions
[ElectriciansForums.net] 16mm SWA tails maybe 9 mtrs from isolator on a 100a supply, and other concerns - EICR opinions
 
You are assesong the job as per BS7671, nithing else so UKPN has no bearing on it.
I was under the impression for BS7671 you have to have fault protection for all cables, and overcurrent where necessary.
Overcurrent has been dealt with through assessement of max demand for the installation.
The fault protection for the tails is only by permission with UKPN, so if UKPN has no bearing, surely that means it would be unsatisfactory by default due to no valid fault protection? If they only allow 3m if they are happy for their fault protection to be used, then that's that?
 
I was under the impression for BS7671 you have to have fault protection for all cables, and overcurrent where necessary.
Overcurrent has been dealt with through assessement of max demand for the installation.
The fault protection for the tails is only by permission with UKPN, so if UKPN has no bearing, surely that means it would be unsatisfactory by default due to no valid fault protection? If they only allow 3m if they are happy for their fault protection to be used, then that's that?

I thought the same until I read through a load of posts.

IET Forums - EICR - https://www.------.org/forums/forum/messageview.cfm?catid=205&threadid=70233

"
Not BS7671 as such, but in the paperwork from a well know DNO..
If you want connection, you need ot do what they ask for.

4.6 Meter Tails
Standard 25mm2 copper double-insulated conductors (meter tails) from the meter to the cut-out shall be provided and installed by the appointed meter operator.
Standard 25mm2 copper double-insulated conductors shall be provided and installed by the customer from the consumer unit for connection by the meter operator into the outgoing (load side) of the meter.
BS 7671 Regulation 433.2.2 requires a maximum three metres distance between overload protection devices and their source, therefore the customer shall provide and install an intermediate switch fuse or isolating switch if the distance between the meter and consumer unit is greater than three metres.
The customer should seek professional electrical advice to determine the protection equipment that is appropriate for the customer given the impedance at the cut-out and the design of their installation as UK Power Networks is unable to advise on these aspects.
Meter tails shall not be installed or run inside the cavity wall of a building other than passing directly through the wall.
Tri-rated cables shall not be terminated onto UK Power Networks equipment.



quoted from page 6 of the
ENGINEERING DESIGN STANDARD EDS 08-0129
LV CUSTOMER SUPPLIES UP TO 100A SINGLE PHASE
"
 

Reply to 16mm SWA tails maybe 9 mtrs from isolator on a 100a supply, and other concerns - EICR opinions in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

Joined
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
16mm SWA tails maybe 9 mtrs from isolator on a 100a supply, and other concerns - EICR opinions
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28
Unsolved
--
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top