This has come up many times before and after a couple of hours reading previous posts I'm no closer to deciding on a code, note or nothing at all.

BS7671 allows 16mm tails on 100A fuse if demand is less than the cables CCC, I have 16mm at 94amps and the max demand is 60a.

From a previous post I've read UKPN state switched fuse OR ISOLATOR within 3mtrs.

Would you code, mention or no mention this?
 
maximum three metres distance between overload protection devices and their source, therefore the customer shall provide and install an intermediate switch fuse or isolating switch if the distance between the meter and consumer unit is greater than three metres.
Yeah I've always thought that's ridiculous too, basically the DNO just want a way to remove all load before pulling their fuse. Then someone got confused about something else, and decided to imply that an "isolating switch" gives overcurrent protection.
In this case, there is an isolating switch, so the DNO's requirements have been met technically...
 
I was under the impression for BS7671 you have to have fault protection for all cables, and overcurrent where necessary.
Overcurrent has been dealt with through assessement of max demand for the installation.
The fault protection for the tails is only by permission with UKPN, so if UKPN has no bearing, surely that means it would be unsatisfactory by default due to no valid fault protection? If they only allow 3m if they are happy for their fault protection to be used, then that's that?
But there is potential for overcurrent as there isnt just OCPD before the DB where there are several, so as it stands the cable coild become overloaded.
 
I was under the impression for BS7671 you have to have fault protection for all cables, and overcurrent where necessary.
Overcurrent has been dealt with through assessement of max demand for the installation.
The fault protection for the tails is only by permission with UKPN, so if UKPN has no bearing, surely that means it would be unsatisfactory by default due to no valid fault protection? If they only allow 3m if they are happy for their fault protection to be used, then that's that?
But there is potential for overcurrent as there isnt just OCPD before the DB where there are several, so as it stands the cable coild become overloaded.
 
But there is potential for overcurrent as there isnt just OCPD before the DB where there are several, so as it stands the cable coild become overloaded.
good point (I'm not a spark) so both would need to be dealt with by the grace of the DNO.
I'm glad I don't have to do EICRs, it's one thing knowing what will definitely comply and installing it, but it's completely different judging whether something already there complies.
 
Correct - or not so!

I'd have installed metal switched fuses at 80A to enclose SWA conductors and offer protection.

How would you code?
This is a rudimentary issue and how I would Code it is not important. How are you assessing circuit protection for a distribution circuit is provided considering you do not know the characteristics of the protective device and whether this device is recommended for circuit protection of the consumers supply.
 
Main earth uses gas supply
Sorry bit confused with that. Looks like the main earth is coming from the cut out? And the SWA are you absolutely sure it is 16mm and not 10mm? I know it is difficult sometimes to assess cable size especially through a piccy. I agree I would have fitted a couple of maybe Lewden fused isolators maybe 63a cartridge fuses apart from a lack of room and location.
 
A ze of 0.14 ohms will ‘blow’ the fuse whether it be rated at 60,80 or 100 amp bs1361 or bs 88.
I find it harsh to say a C2 as the fuse would blow in less than 5 seconds on a TN system.
However you are only allowed to rely upon the distributors fuse where they allow that it can afford protection to the part of the installation between the origin and the main distribution point where overload and fault protection is provided at your DB.
So if they only allow 3 meters then you need to code accordingly in my opinion.

As for 16 mm on a 100amp fuse.
My opinion is that is the demand of the installation at time of inspection reveals that overload isn’t likely then I’d assess it on that basis.
If the demand was to change in the future then before any alterations in the future by an electrician, they would need to assess the existing demand and decide if it is acceptable to determine if the proposed alterations comply Which is what’s always required anyway.
 
Last edited:
Providing it is 16mmSQ as in the pics it looks like 10. 16mmSQ armoured Is good at 35m clipped direct for 100a. And providing the ZsDB is ok which you have proven there is not code relevent.
However I Disagree with only basic insulation in the meter enclosure, as meter readers have access and as such aren't competent. I'd C2 it on this count under section 526.

Could of staggered the isolators in the box, glanded the inner sheath to a small enclosure box flush with the bottom of the isolator with the top cut out.
 
Sorry bit confused with that. Looks like the main earth is coming from the cut out? And the SWA are you absolutely sure it is 16mm and not 10mm? I know it is difficult sometimes to assess cable size especially through a piccy. I agree I would have fitted a couple of maybe Lewden fused isolators maybe 63a cartridge fuses apart from a lack of room and location.
If i recall correctly the dno around here get right funny if you install something in the meter / cutout cabinet. I fitted a switched fuse for a cu change as the customer wanted it moved somewhere out of sight and they went right off on one when they came to pull the fuse so i coudl fit it in and do the change.... telling me we arent allowed to put stuff in the cabinet. its different if its indoors on a wall then its a free for all.
 

Reply to 16mm SWA tails maybe 9 mtrs from isolator on a 100a supply, and other concerns - EICR opinions in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

Joined
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
16mm SWA tails maybe 9 mtrs from isolator on a 100a supply, and other concerns - EICR opinions
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28
Unsolved
--
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top