I did a board change a couple months ago - everything hunky dory.
Got a call back to same house last week, asked the guy what was wrong. He said the shower wasn't working. I asked what actually was happening with the shower?
"Some smoke" was the reply. :confused:
A "friend of the family" had changed the guys shower since my board change.
Cover off, the neutral was black instead of blue.... crispy and brittle insulation. A little tug and it just falls out the terminal block. Same with the c.p.c.
Pulled spare cable out the wall, new bit of block, reterminated, tested and everything good again.

Sorry, no photos. But it shows you how easy a loose termination can start overheating, and may, in the right circumstances, cause a serious fire.
Hope you charged him, did he start to blame you for the problem? bet the answer is in the affirmative, be surprised if it isn't.
 
He paid me over what I asked for because I came out so quick.
He didn't blame me at all... he blamed his "family friend"
Good customer, and hopefully i'll get more work from him as he's lost trust in getting non-qualified people in
 
He paid me over what I asked for because I came out so quick.
He didn't blame me at all... he blamed his "family friend"
Good customer, and hopefully i'll get more work from him as he's lost trust in getting non-qualified people in
get the guy who installed the shower to come back round, grab him by the finger, and push his finger the wrong way and try to make it touch his wrist, see if he still wants to be an electrician after that
 
Heres one I looked at just last week.. I was only checking out cooker circuit tripping rcd and big melted hole in kitchen rfc fuse holder!! Thought it was an overload at first but no, just loose phase wires. [ElectriciansForums.net] Image showing effects of consumer unit fire!

[ElectriciansForums.net] Image showing effects of consumer unit fire!
 

Reply to Image showing effects of consumer unit fire! in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
843

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top