Went to a job to check out a fault on an outhouse. Turns out that the outhouse is supplied via a 2.5mm T&E from the main house CU, which runs for several meters along an external wall (outside and unprotected) then disapears into a 50mm plastic pipe underground. The good bit is that at the other end (a post on which there is a metal box) the cable miraculously turns into a rubber 3core + earth.
Now I know these cables are running in mechanical protection (no idea of depth) and I understand that there must be a joint somewhere along the route, but from a basic level is 2.5mm T&E running outside then going into buried conduit really compliant with regs?
I can't find where it isn't but a seasoned Spark tells me it's not compliant.
Any non sarcastic reply warmly welcomed. ;)
 
The fact that degradation has occurred proves, in my opinion, that it doesn’t comply as an installation method.
If nothing else the ref about good workmanship and materials etc hasn’t been complied with.
 
The fact that degradation has occurred proves, in my opinion, that it doesn’t comply as an installation method.
If nothing else the ref about good workmanship and materials etc hasn’t been complied with.

True, but there are countless numbers of installations like these and even when picked up as issues on EICR’s owners don’t have to do anything about them ......
 
Apart from lack of UV protection (which could have been sorted with a lick of paint), there’s the hidden joint.
Of course, if it’s an acceptable MF joint, then.....
 
We were discussing the use of twin & e for outside in another thread, where @Pete999 posted a video.
It does appear that the OSG does suggest that it can be ok.

[ElectriciansForums.net] Can't find a reg on it, but it just seems wrong...
 
What where the test results.

You can’t mark down an installation because you don’t like the look of it!

Bobgeldof - so you’ve given me a dumb ..... what’s your opinion

I’ve lost count of the amount of people that have ignored any comments or advice on improvements I have given.....
 
OK! A bit of a filler for you... whole story.
See picture below.
The cable I mentioned above goes to a metal box on a post. From there it supplies an outhouse (as mentioned) and some stables some 40m away.
The outhouse is subsequently fed witha 2core and Earth rubber cable which is jointed within the outhouse to a 2.5mm T&E (which also had faults).
The stables were supplied from a cable I don't recall seeing before (see picture). It is a 20mm almost solid pvc cable with a solid core conductor. They had used one for the live and one for the neutral so there were two cables running the 40m to the stables. No earth and I haven't yet checked for an earth spike.
[ElectriciansForums.net] Can't find a reg on it, but it just seems wrong...
 
True, but there are countless numbers of installations like these and even when picked up as issues on EICR’s owners don’t have to do anything about them ......
That is their choice, as long as the Report is concise and accurate it is not your problem.
We were discussing the use of twin & e for outside in another thread, where @Pete999 posted a video.
It does appear that the OSG does suggest that it can be ok.

View attachment 43241
It does not suggest it can be left exposed to the elements or mechanical stress.
 
OK! A bit of a filler for you... whole story.
See picture below.
The cable I mentioned above goes to a metal box on a post. From there it supplies an outhouse (as mentioned) and some stables some 40m away.
The outhouse is subsequently fed witha 2core and Earth rubber cable which is jointed within the outhouse to a 2.5mm T&E (which also had faults).
The stables were supplied from a cable I don't recall seeing before (see picture). It is a 20mm almost solid pvc cable with a solid core conductor. They had used one for the live and one for the neutral so there were two cables running the 40m to the stables. No earth and I haven't yet checked for an earth spike.
[ElectriciansForums.net] Can't find a reg on it, but it just seems wrong...
 

Reply to Can't find a reg on it, but it just seems wrong... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
725

Similar threads

  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
653
  • Question
There are two reasons for a fuse/mcb they are: 1) fault conditions - which must exist always, and be capable of operating for all points on the...
Replies
4
Views
917

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top