It does not suggest it can be left exposed to the elements or mechanical stress.
Hi - I've opened BBB for the first read - Reg 522.8.10 is the same as before. It roughly says if it's not SWA then it needs to be in conduit or ducting that provides equivalent mechanical protection. Just my take on it, but 50mm plastic drain pipe (I guess that's what they've used) wouldn't pass muster as mechanical protection equivalent to SWA.... the outhouse is supplied via a 2.5mm T&E from the main house CU, which runs for several meters along an external wall (outside and unprotected) then disapears into a 50mm plastic pipe underground ... but from a basic level is ... T&E ... into buried conduit really compliant with regs? I can't find where it isn't ...
Hi - I've opened BBB for the first read - Reg 522.8.10 is the same as before. It roughly says if it's not SWA then it needs to be in conduit or ducting that provides equivalent mechanical protection. Just my take on it, but 50mm plastic drain pipe (I guess that's what they've used) wouldn't pass muster as mechanical protection equivalent to SWA.