FYI
Copy of email from Basec.
Thanks for your enquiry via our website.
The situation on SY CY etc. has been updated since our previous release, and there is now a tougher line being taken against the use of these cables.
There is now a specific paragraph in the On Site Guide to the IET Wiring Regulations BS 7671 Amendment 3 (the current edition), which is the practical guide registered electricians are expected to follow, and which states the following:
———
7.9 Installation and use of non-standard cables
For the purposes of this guidance publication and ensuring compliance with BS 7671, the installation and use of non-standard cables, such as SY, CY and YY cables is discouraged.
The letters signify:
S – steel braid
Y – PVC
C – copper braid
To identify:
SY cables - steel braided, usually translucent sheath, PVC insulated flexible conductors
YY cables – usually grey PVC sheath, PVC insulated flexible conductors
CY cables – tinned copper wire braid, usually grey PVC sheath, PVC insulated flexible conductors
To meet the requirements of BS 7671, every item of equipment must comply with a British or Harmonized Standard, in the absence of such, reference can be made to IEC standards or the appropriate standard of another country.
SY, YY and CY cables are not made to British or Harmonised Standards. Some manufacturers state that their cables “generally” comply with a British Standard; this is not deemed sufficient for the purposes of BS 7671.
It is important that cables have approval from an independent testing organisation and installers should ensure that all cables purchased have manufacturers’ identification and a specification reference/standard number printed on the sheath to enable testing, if necessary, and traceability.
———
SY, YY or CY cables are not made such that their construction, materials, voltage rating, temperature rating or performance claims to conform fully to any British or Harmonised standard, or indeed to international or other national standards. Different suppliers sometimes make a number of claims that the cables conform ‘generally to’ particular standards / specifications, but these are invariably unsubstantiated and in fact the cables cannot conform to various aspects of the quoted specifications. Because of the lack of specification these cables can and will be of variable construction and performance, and a purchaser / supplier should be very wary, particularly of making recommendations. We are not aware of any such cables that have independent testing or approval.
There are specific and onerous engineering assessment procedures in the Wiring Regulations where it is proposed to use non-standardised products. Most electricians would not have the knowledge to conduct such assessments or keep the appropriate records.
I also attach for your information a short guidance note published by the ECA on the topic.
The key clauses in the IET wiring regulations are 133.1.1, 133.1.3 and 511.1, 511.2.
If you require further information please contact us again. My colleague Simon Brown can deal with many installation issues.
Best regards,
Dr Jeremy Hodge
Chief Executive