The only thing you'd need to do to HO7RN would be to put crimps on the terminations as it's fine stranded, other than that, fill yer boots man. Idiots will always walk among us, we can't see into the future except to use common sense today. Besides, I've lost count of the number of submains run in 16mm t+e through all kinds of spaces where it could be argued something else would have been better. If you're only running 32-40A then I'd suggest 10mm 5c HO7 is plenty overkill.
 
here's a datasheet for you......
 

Attachments

  • h07rn-f-bs-en-50525-2-21-flexible-rubber-cable.pdf
    118.1 KB · Views: 16
The only thing you'd need to do to HO7RN would be to put crimps on the terminations as it's fine stranded, other than that, fill yer boots man. Idiots will always walk among us, we can't see into the future except to use common sense today. Besides, I've lost count of the number of submains run in 16mm t+e through all kinds of spaces where it could be argued something else would have been better. If you're only running 32-40A then I'd suggest 10mm 5c HO7 is plenty overkill.
Your preaching to the converted.

I did a job in SWA last year, 35mm 5 core 160A supply, I had fitters and toolmaker conscripted in to help me pull it in.

I vowed from then, that ho7 would be my new cable of choice, I think it is actually more robust than SWA, especially in the bigger sizes.
 
Although the spec for 16mm NYY states 'solid core' I was right to not believe it. A sample arrived today. 16mm, at least, is definitely stranded, strips really easily, and looks easy to work with.
[ElectriciansForums.net] 3Ph sub-mains supplied via 5-core NYY, not SWA. OK or not?

[ElectriciansForums.net] 3Ph sub-mains supplied via 5-core NYY, not SWA. OK or not?

So I'm going to go with the NYY at £6.77/m rather than H07RN which is £10.17/m.
Many thanks for all the helpful advice.
 
Hi - it would be good to confirm the conductor types as the specs I looked at seemed to say NYY was a solid conductor per core even at 16mm. ...
Thanks Wilko, but look at my pictures immediately above.
I too read that 'solid core' spec, but didn't believe it, so ordered a 1m sample.
The specs are wrong.
 
FYI

Copy of email from Basec.

Thanks for your enquiry via our website.

The situation on SY CY etc. has been updated since our previous release, and there is now a tougher line being taken against the use of these cables.

There is now a specific paragraph in the On Site Guide to the IET Wiring Regulations BS 7671 Amendment 3 (the current edition), which is the practical guide registered electricians are expected to follow, and which states the following:

———

7.9 Installation and use of non-standard cables

For the purposes of this guidance publication and ensuring compliance with BS 7671, the installation and use of non-standard cables, such as SY, CY and YY cables is discouraged.
The letters signify:

S – steel braid
Y – PVC
C – copper braid

To identify:
SY cables - steel braided, usually translucent sheath, PVC insulated flexible conductors
YY cables – usually grey PVC sheath, PVC insulated flexible conductors
CY cables – tinned copper wire braid, usually grey PVC sheath, PVC insulated flexible conductors

To meet the requirements of BS 7671, every item of equipment must comply with a British or Harmonized Standard, in the absence of such, reference can be made to IEC standards or the appropriate standard of another country.

SY, YY and CY cables are not made to British or Harmonised Standards. Some manufacturers state that their cables “generally” comply with a British Standard; this is not deemed sufficient for the purposes of BS 7671.

It is important that cables have approval from an independent testing organisation and installers should ensure that all cables purchased have manufacturers’ identification and a specification reference/standard number printed on the sheath to enable testing, if necessary, and traceability.

———


SY, YY or CY cables are not made such that their construction, materials, voltage rating, temperature rating or performance claims to conform fully to any British or Harmonised standard, or indeed to international or other national standards. Different suppliers sometimes make a number of claims that the cables conform ‘generally to’ particular standards / specifications, but these are invariably unsubstantiated and in fact the cables cannot conform to various aspects of the quoted specifications. Because of the lack of specification these cables can and will be of variable construction and performance, and a purchaser / supplier should be very wary, particularly of making recommendations. We are not aware of any such cables that have independent testing or approval.

There are specific and onerous engineering assessment procedures in the Wiring Regulations where it is proposed to use non-standardised products. Most electricians would not have the knowledge to conduct such assessments or keep the appropriate records.

I also attach for your information a short guidance note published by the ECA on the topic.

The key clauses in the IET wiring regulations are 133.1.1, 133.1.3 and 511.1, 511.2.

If you require further information please contact us again. My colleague Simon Brown can deal with many installation issues.

Best regards,

Dr Jeremy Hodge
Chief Executive

cid:[email protected] +44 (0)1908 267300
cid:[email protected] +44 (0)7900 505950
cid:[email protected] +44 (0)1908 267255
cid:[email protected] [email protected]
cid:[email protected] www.basec.org.uk
 
It seems quite certain that from the above that the cable would not be compliant with BS7671. In which case the certificate you would be issuing should state the departure from regulations. You say it is going via a loft. I imagine that would mean it is going through insulation? In which case the CCC rating would be halved (circa). In a cold winter where the gas fired(?) heating fails and heaters are used you may well get to the top of what the installation you are proposing can safely accommodate. What route does the supply to the DB for the annexe take? Personally for the above reasons I would not use the cable you are using and would opt for SWA as being a no brainer as it does comply with BS7671 subject to the route taken and also the type of supply. i.e. is it TNS etc? In designing an installation account should be taken of future use and if it were used for say a granny annexe and cookers and electric showers were installed would the existing supply be able to meet that change of use. Of course there are many factors I do not know of related to that so this is conjecture or an educated guess on some of the downsides to what you are proposing.
 
It seems quite certain that from the above that the cable would not be compliant with BS7671


NYY does comply as it is to an IEC standard which the regs do say we can use-infact the paragraph stating this is in the middle of Charlie's post above. So it does not need to go down as a departure. It is not the same as CY, YY, SY.
 
NYYJ is not the same as CY SY and YY, just because it uses the same letters it doesn't necessarily not comply.

You can see in this data sheet that it does comply with international and BS EN standards.
 

Attachments

  • [ElectriciansForums.net] 3Ph sub-mains supplied via 5-core NYY, not SWA. OK or not?
    Screenshot_20190610_065422_com.google.android.apps.docs.jpg
    453.3 KB · Views: 15
FYI

Copy of email from Basec.

Thanks for your enquiry via our website.

The situation on SY CY etc. has been updated since our previous release, and there is now a tougher line being taken against the use of these cables.

There is now a specific paragraph in the On Site Guide to the IET Wiring Regulations BS 7671 Amendment 3 (the current edition), which is the practical guide registered electricians are expected to follow, and which states the following:

———

7.9 Installation and use of non-standard cables

For the purposes of this guidance publication and ensuring compliance with BS 7671, the installation and use of non-standard cables, such as SY, CY and YY cables is discouraged.
The letters signify:

S – steel braid
Y – PVC
C – copper braid

To identify:
SY cables - steel braided, usually translucent sheath, PVC insulated flexible conductors
YY cables – usually grey PVC sheath, PVC insulated flexible conductors
CY cables – tinned copper wire braid, usually grey PVC sheath, PVC insulated flexible conductors

To meet the requirements of BS 7671, every item of equipment must comply with a British or Harmonized Standard, in the absence of such, reference can be made to IEC standards or the appropriate standard of another country.

SY, YY and CY cables are not made to British or Harmonised Standards. Some manufacturers state that their cables “generally” comply with a British Standard; this is not deemed sufficient for the purposes of BS 7671.

It is important that cables have approval from an independent testing organisation and installers should ensure that all cables purchased have manufacturers’ identification and a specification reference/standard number printed on the sheath to enable testing, if necessary, and traceability.

———


SY, YY or CY cables are not made such that their construction, materials, voltage rating, temperature rating or performance claims to conform fully to any British or Harmonised standard, or indeed to international or other national standards. Different suppliers sometimes make a number of claims that the cables conform ‘generally to’ particular standards / specifications, but these are invariably unsubstantiated and in fact the cables cannot conform to various aspects of the quoted specifications. Because of the lack of specification these cables can and will be of variable construction and performance, and a purchaser / supplier should be very wary, particularly of making recommendations. We are not aware of any such cables that have independent testing or approval.

There are specific and onerous engineering assessment procedures in the Wiring Regulations where it is proposed to use non-standardised products. Most electricians would not have the knowledge to conduct such assessments or keep the appropriate records.

I also attach for your information a short guidance note published by the ECA on the topic.

The key clauses in the IET wiring regulations are 133.1.1, 133.1.3 and 511.1, 511.2.

If you require further information please contact us again. My colleague Simon Brown can deal with many installation issues.

Best regards,

Dr Jeremy Hodge
Chief Executive

cid:[email protected] +44 (0)1908 267300
cid:[email protected] +44 (0)7900 505950
cid:[email protected] +44 (0)1908 267255
cid:[email protected] [email protected]
cid:[email protected] www.basec.org.uk

NYYJ is not the same as CY SY YY, it does comply with IEC and BS EN standards therfore does comply with BS7671.

Just because the same letters are used in its identifier it doesn't make it the same cable,
 
NYY is nonetheless available from brands that are independently tested and certified by a European recognised body such as VDE. Apart from the stranding, it differs in construction from flexible control cables in that the insulation is of the same order of radial thickness and strength as T+E etc, while the insulation of CY for example is thinner and arguably less durable.

It's popular in mainland Europe where circular cables with all cores equal and insulated are the norm instead of T+E. I'm working in Estonia at the moment and will be going to the Bauhaus later to get some NYY to relocate my lighting dimmers.
 
therfore does comply with BS7671
The only reference that I can find referring to IEC standards is the preface of BS7671. I do not read anything that explicitly states that NYY cable is compliant or acceptable. It seems to be in a realm where it is very moot. The particular standard referred to by @davesparks has also attached to it the letter -J what is that. In essence what I am saying is it is not absolutely clear that it is or is not kosher. What are we to make from the below? I do know that if I am required to comply with BS7671 it is going to be far less of a headache to use SWA. It seems far too complex and nebulous to say hand on heart that NYY is compliant. The standards referred to only refer to fire standards.

Where the above documents contain UK special national conditions, those conditions have been incorporated within BS 7671. If BS 7671 is applied in other countries the above documents should be consulted to confirm the
status of a particular regulation.
BS 7671 will continue to be amended from time to time to take account of the publication of new or amended CENELEC and IEC standards. The opportunity has been taken to revise regulations that experience has shown require clarification or to allow for new technology and methods.
 
133.1.1 Every item of equipment shall comply with the appropriate British or Harmonized Standard. In the absence of such a standard, reference shall be made to the appropriate International (IEC) standard or the appropriate standard of another country.
And how exactly may I do that without reading the appropriate standards if I could afford them and have several years to read them all? It is quite enough to handle the actual installation principles and practices working within the regulatory and legal framework we do know applies. But when you are talking endless standards of other countries it is difficult if not impossible to be certain.
 

Reply to 3Ph sub-mains supplied via 5-core NYY, not SWA. OK or not? in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top