I was called out to a fault today where the newly fitted consumer units RCD was tripping when the cooker was switched on.The cooker had been checked by an appliance engineer and deemed to be fully working with no faults.
So I turned up to be presented with a nice new shiny MK metal clad dual RCD board.Upon removing the lid I was presented with this
[ElectriciansForums.net] Where do these cowboys come from?


Also notice the top of the board as below....



[ElectriciansForums.net] Where do these cowboys come from?


Upon asking about the board change the customer said that they had bought the board and a nice young guy had fitted it for £100!
The board was not labeled what so ever with grommets missing etc.
No paperwork had been supplied and no testing done.

The fault on the cooker was found to be the neutral put in the opposite bar to the one it should have been in.This was quickly rectified but i started to write a list of what was wrong(I am sure there are even more than this)

1.Mains tails not double covered 25mm.
2.Main earth was only 6mm feeding the unit.
3.No grommets or bushes in any holes.
4.Huge hole where tails entered unit (easily stick a finger in there) and no bushed glands for tails.
5.Green/yellow sleeving missing off a lot of earth wires.
6.No mains gas or water bonding.
7.Unit not marked up and no warning labels anywhere.
8.No test certs or Part P supplied.
9.Consumer unit only fixed with 2 screws at the top and none at the bottom so the board was flapping.
10.Old rubber cable still connected(showing a very low neutral to earth fault.
11.A twin and earth with just its earth and neutral connected but not the live with very low tests showing.
12.Mains tails sticking out of main switch with copper showing.
[ElectriciansForums.net] Where do these cowboys come from?


13.Four 2.5mm cables in one breaker.
14.40 amp breaker feeding cooker circuit.(I would have put it on a 32amp)
15.Muliple lighting cables in one breaker.
I am sure there are many more faults that I haven't been bothered to find so feel free to chip in.:p

The customer said "Should I call him back to put it right?"
I said you should only call him back to give him a slap :fearscream:and would not want this guy touching any electric ever again.
I have given the customer a quote to redo the consumer unit again with bonding,testing,certification etc but by the way he was talking about getting the young lad back then I doubt I will be doing anymore work.:angry:
 
I was called out to a fault today where the newly fitted consumer units RCD was tripping when the cooker was switched on.The cooker had been checked by an appliance engineer and deemed to be fully working with no faults.
So I turned up to be presented with a nice new shiny MK metal clad dual RCD board.Upon removing the lid I was presented with thisView attachment 43750

Also notice the top of the board as below....



View attachment 43751

Upon asking about the board change the customer said that they had bought the board and a nice young guy had fitted it for £100!
The board was not labeled what so ever with grommets missing etc.
No paperwork had been supplied and no testing done.

The fault on the cooker was found to be the neutral put in the opposite bar to the one it should have been in.This was quickly rectified but i started to write a list of what was wrong(I am sure there are even more than this)

1.Mains tails not double covered 25mm.
2.Main earth was only 6mm feeding the unit.
3.No grommets or bushes in any holes.
4.Huge hole where tails entered unit (easily stick a finger in there) and no bushed glands for tails.
5.Green/yellow sleeving missing off a lot of earth wires.
6.No mains gas or water bonding.
7.Unit not marked up and no warning labels anywhere.
8.No test certs or Part P supplied.
9.Consumer unit only fixed with 2 screws at the top and none at the bottom so the board was flapping.
10.Old rubber cable still connected(showing a very low neutral to earth fault.
11.A twin and earth with just its earth and neutral connected but not the live with very low tests showing.
12.Mains tails sticking out of main switch with copper showing.View attachment 43753

13.Four 2.5mm cables in one breaker.
14.40 amp breaker feeding cooker circuit.(I would have put it on a 32amp)
15.Muliple lighting cables in one breaker.
I am sure there are many more faults that I haven't been bothered to find so feel free to chip in.:p

The customer said "Should I call him back to put it right?"
I said you should only call him back to give him a slap :fearscream:and would not want this guy touching any electric ever again.
I have given the customer a quote to redo the consumer unit again with bonding,testing,certification etc but by the way he was talking about getting the young lad back then I doubt I will be doing anymore work.:angry:
Domestic Installer, or Cowboy, was he? cus he certainly ain't an Electrician.
 
buy cheap buy twice, obviously this "young guy" hasnt got much experience with the regs, who doesnt upgrade the tails when upgrading a board?!

sorting out crossed neutrals is an easy job, most of the time its visual, although looking in that board id guess visual was out of the question.

no excuse for the shoddy "dressing" of cables, plenty of length on them
 
i like the new hager boards, with the square knockouts with the adaptor for supply tails

i seem to be coming across alot of smoke alarms that dont have permanent lives, just grabbed the switched live from the light fitting " be alright innit" by the time the battery has run dry the fitter is long gone
 
That is down right dangerous... thing is if you reported the stupid kid doing this work to building control etc, you could in theory get the homeowner fined upto £5k.. never heard of the homeowner being fined though but that idiot responsible needs stopping in case he ends up hurting somebody.
 
buy cheap buy twice, obviously this "young guy" hasnt got much experience with the regs, who doesnt upgrade the tails when upgrading a board?!

sorting out crossed neutrals is an easy job, most of the time its visual, although looking in that board id guess visual was out of the question.

no excuse for the shoddy "dressing" of cables, plenty of length on them

I often don't, if the existing 16mm tails are of sufficient length and in good order and the DNO fuse is 60 or even 80 amps I don't see the need. How many domestic installs actually need 25mm tails - especially when the incoming supply is 16mm ?! And 25mm can be a right pain to work with when space is tight....
 
Absolutely terrible job, I mean who in their right mind would fit an MK Consumer Unit?

I recently repositioned one that had been recently [badly] installed by a NIC.... electrical genius. I must say that the steel and particularly the front cover seemed surprisingly thin and flimsy. The much maligned BG boards are far superior IMHO. :)
 

Reply to Where do these cowboys come from? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

Joined
Location
Blackpool,Lancashire.
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)