RCBO for old Square D distribution board | on ElectriciansForums
Guest viewing is limited

Discuss RCBO for old Square D distribution board in the UK Electrical Forum area at ElectriciansForums.net

soms

-
Trainee
Joined
Mar 3, 2014
Messages
89
Reaction score
49
Location
Somerset
Hi,
A relative has moved into a flat with a mid-80's Square D QO1 12F distribution board, which has MCBs on all outgoing ways.

There are proposals to update the kitchen with a desire for some additional socket outlets. To meet the requirements of Part P and by extension, BS 7671, RCD protection will be required and the simplest way to implement this would be to find a way of providing it for the entire ring final circuit supplying the socket outlets.

My thinking is to install a 32 A RCBO in place of the original MCB, if I can get something electrically compatible with the DB.
I removed an existing MCB (though a later addition itself) to see what fits in this board, and it is the 'clip' type bus bar connection.

I have seen some 'clip' type Square D and Schneider Electric RCBOs for sale on eBay, but just wanted an opinion as to whether there is anything else I should be aware of in terms of product compability before committing to buy something?

The installation has a TN earthing system (the supply to the DB coming from a separate meter room), I haven't measured the Zs on the circuit but of course should bear this in mind as in some cases B type breakers are not easy to get whereas C types are.

Pics attached.
Thanks.

[ElectriciansForums.net] RCBO for old Square D distribution board


[ElectriciansForums.net] RCBO for old Square D distribution board
 
Schneider do protective devices that fit in old boards we had a 3 phase old D.B. with MCB's same as those that had to be de-rated to 20A. On Monday give their technical department a call give them all the info of existing inc protective devices. Not sure of the cost as non-stocked items at wholesalers like this usually aren't heavily discounted.
 
The protective devices at that board are BS3871 type 4 code No. QOH-X. These have never been recognised by any version of the wiring regulations but this does not mean they are not suitable to provide suitable circuit protection however, type 4 devices are not considered suitable for the protection of general socket outlets and in modern terms for any circuit in a domestic premises. Schneider who took over Square D have to their credit produced compatible devices and for a type B 32A rcbo you require part no. QO132B1ORCBO30F.
 
The protective devices at that board are BS3871 type 4 code No. QOH-X. These have never been recognised by any version of the wiring regulations but this does not mean they are not suitable to provide suitable circuit protection however, type 4 devices are not considered suitable for the protection of general socket outlets and in modern terms for any circuit in a domestic premises. Schneider who took over Square D have to their credit produced compatible devices and for a type B 32A rcbo you require part no. QO132B1ORCBO30F.
I am liking schneider more and more of late, the stuff they make via the many brands in the stable are pretty well made, not too pricey and the tech team are on the ball. Schneider are now my go to instead of Hager.
 

They are fantastic prices for them, there was a point we were paying up to £100 plus VAT for them from Edmunsons. Alot of schools have these boards in and we used to always find a few they didnt meet disconnection times. Schneider still make the RCBOs to fit.
 
fit a stand alone RCD alongside the DB. feed from existing MCB and N, with 6.0mm, then on to RFC. ( divert the RFC legs from MCB to RCD.).
 
Schneider do protective devices that fit in old boards we had a 3 phase old D.B. with MCB's same as those that had to be de-rated to 20A. On Monday give their technical department a call give them all the info of existing inc protective devices. Not sure of the cost as non-stocked items at wholesalers like this usually aren't heavily discounted.

Thanks for the advice, it is nice to know you can actually make contact with a manufacturer and get sense from them if required.

The protective devices at that board are BS3871 type 4 code No. QOH-X. These have never been recognised by any version of the wiring regulations but this does not mean they are not suitable to provide suitable circuit protection however, type 4 devices are not considered suitable for the protection of general socket outlets and in modern terms for any circuit in a domestic premises. Schneider who took over Square D have to their credit produced compatible devices and for a type B 32A rcbo you require part no. QO132B1ORCBO30F.

@westward10 thank you for this information, that is very useful to know.
Thanks for quoting the correct part number, I have had a quick look online and they seem expensive to purchase, which is understandable.

fit a stand alone RCD alongside the DB. feed from existing MCB and N, with 6.0mm, then on to RFC. ( divert the RFC legs from MCB to RCD.).

@telectrix that is a good idea which had not occurred to me, it would be a cheaper way to get around it and there is plenty of room below the board to do it.

Given what @westward10 said, do you think I should be concerned about the existing MCB with respect to meeting the disconnection times, which is for fault protection (using ADS) if I recall? I am away from home so do not have my books to hand to check on what can be considered to be provided by the RCD, which otherwise is offering additional protection. I am now a third year apprentice so the details of BS 7671 are not fully committed to memory yet. To be made a little more complicated to commit with the upcoming switch to the 18th Edition.

Thank you for all the useful input :)
 
Maximum Zs values for Type 4 devices have never been quoted in the Regulations so you have to refer to manufacturers figures. Type 4 devices unlike other circuit breakers used 0.4 and 5 sec disconnection times, so 0.4 for socket outlets and 5 sec for fixed equipment.
 
It may get to a point that if any further additions/work is carried out and requires RCD/RCBO protection a new consumer unit would be cheaper in the long run if the prices are too high eg a BG 5 +5 split £73 inc VAT.
 

Reply to RCBO for old Square D distribution board in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
922
  • Question
Ye smaller board (containing the RCBO'S) will literally be next to the MEMSHIELD, And hence the 32A MCB be simply feeding power to a 32A RCBO I...
Replies
5
Views
2K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top