Hey guys, just wondering if this installation is ok? the neutral can get isolated on the main circuit which if the second circuit is not isolated would mean there is no return for the second circuit. the isolator switches are individual, each iso switch switches the L and N at the same time (its actually two isolators in one shell)

[ElectriciansForums.net] Is this meter installation ok?
 
If things are as your diagram, then all is well, but your text throws doubt on whether it really is a four pole isolator.
It's quite common for multipole lever operated devices to be made up of single pole devices riveted together with a crimped on profile or a pin linking all the levers together, so that they all operate together.
 
If the markings are as you say above, then it does look like it's two separate isolators, in which case the neutral block should be between the meter and isolators, with a neutral fed to each isolator.
 
yeah so this is the way i would do it but one of the guys said you can do it the diagram way if for whatever reason its not possible to. im not sure it sits well with me if the iso can be independently switched. im thinking maybe heat build up at the switched lines terminations
 
If the isolators are independent of each other, then the way it is wired in your diagram is unsatisfactory and dangerous for the reason you said in your OP.
 

Reply to Is this meter installation ok? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
717
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Hi all, first post, please be gentle ;) Iv been involved in a bathroom refurb, nothing major, moving a light fitting and switch. My problem came...
Replies
0
Views
263
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
578

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top